Relating to CRR sounds reasonable.  Is there anything threadable that has a
CRR of 1 or greater that is not sched 40?  Wheatland GL is 0.61 to 0.25 for
1"-2" for example.  XL has virtually the same ID but no CRR listed but it
must be the same as GL.  

Now Dyna Thread is interesting.  CRR stated of 1 but 3.6% larger ID than
sched 40.  Not sure I follow that though. If the wall is less than sched 40
how can it have a CRR of 1?  If it's 3.6% less seems based on the formula
CRR = (X/X40)^3 should be a CRR of about 0.9.  OK that's much better than
0.61 BUT it's NOT 1.  

Chris Cahill, P.E.
Fire Protection Engineer
Sentry Fire Protection, Inc.
 
763-658-4483
763-658-4921 fax
 
Email: [email protected]
 
Mail: P.O. Box 69
        Waverly, MN 55390
 
Location: 4439 Hwy 12 SW
              Waverly, MN 55390
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ed Kramer
Sent: Wednesday, June 16, 2010 4:52 PM
To: [email protected]
Subject: threaded thinwall hanger spacing

Max hanger spacing is covered in section 9.22 and Table 9.2.2.1(a) (NFPA 13
2010).  Threaded thinwall pipe has a max hanger spacing less than other
steel pipe in sizes 1 1/2" to 3". 

 

Maybe I'm just not seeing it, but is there a clear definition of "thinwall"?
I've always assumed it meant any pipe with a wall thickness less than sched
40/sched 30.  Today I read the commentary in the handbook that follows
9.2.2.1 - it says hangers on threaded thinwall need to be spaced closer
together "because of the reduced remaining pipe wall thickness between the
inside diameter and the thread root diameter".  That sounds very similar to
Corrosion Resistance Ratio (CRR).  

 

So if my threaded "thinwall" has a CRR of 1.0 or greater, is it "thinwall"
in the context of 9.2.2.1?  In other words, does the reduced hanger spacing
apply?

 

Ed Kramer

Littleton, CO

 

 

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to