Per Dyna-Thread's data sheet, CRR is ". . . the calculated wall thickness AT
THE BASE OF THE FIRST EXOSED THREAD, ASSUMED TO BE THE WEAKEST POINT OF THE
PIPE LENGTH.  Dyna-Thread and sch-40 have the same calculated wall thickness
at this point and are both assigned the same CRR of 1.00."  *Capital letters
added by me*

I really don't understand the 'how' of why some threadable thinwalls have a
CRR of 1, but some do.  I'm curious if a CRR of 1 allows that particular
pipe to use increased hanger spacing (equal to that of sched 40).  If this
were a 'listing' question, I'd call Tyco.  But this seems to be more of an
interpretation of section 9.2.2.1.

Ed Kramer
Littleton, CO



> 
> Well let me be more clear CRR is based on wall thickness.  Corrosion is
> much
> more complex when the chemistry of the pipe is different.  CRR does not
> tell
> the story of corrosion but as best I know it's the only thing we have to
> put
> our hand on besides WAG.
> 
> Chris Cahill, P.E.
> Fire Protection Engineer
> Sentry Fire Protection, Inc.
> 