Heh,

How old is that bet?

Benjamin Young



On Thu, Jun 17, 2010 at 4:07 PM, Reed Roisum <[email protected]> wrote:

>
> So there is a use for differential equations.  WOW.  Guess I need to pay
> up.
>
>
> Reed A. Roisum, CET
> Ulteig Engineer, Inc.
> Engineering Technician
>
>
> Direct: (701)280-8580
> Cell: (701)212-8810
>
>
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Law, Kevin W
> Sent: Thursday, June 17, 2010 2:33 PM
> To: [email protected]
> Subject: RE: Gravity Tanks
>
> Of course depending how high the tank is mounted in relation to the level
> of discharge the available head will vary which will affect the rate of
> discharge.......seems to me from my college days(now becoming only a distant
> memory) that this would be an excellent example for the use of differential
> equations to solve for the actual performance of the system over time.
>  ............Sounds like a good thing to have an intern figure up for ya'
>
>
>
>
> Kevin Law, PE
> Bechtel National, Inc.
> Waste Treatment Project
> Fire Protection Engineering
> Work  (509) 371-3280
> Cell    (509) 531-5715
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, June 17, 2010 10:57 AM
> To: [email protected]
> Subject: Re: Gravity Tanks
>
> Art,
>
> The reason to assume it is empty is because it might be at the end of your
> required duration without replenishment. Of course if when it's full the
> capacity is twice the duration then you can figure it at half empty. If
> there is replenishment at you know the rate you can add that to the mix and
> perhaps at the end of duration it would only be 2/5ths empty. Each tank has
> to be calculated to friction loss and elevation as you say but if you don't
> have all the pertinent values, most of which were not stated in the original
> post (duration, capacity, replenishment rate) then you have to assume you
> start with an empty tank for calculation purposes.
>
> On Thu, Jun 17, 2010 at 8:04 AM, Art Tiroly <[email protected]>
> wrote:
> > Is this tank dedicated for fire protection? Why would you assume it is
> > empty? Then the water is only available for 1 minute while you empty
> > the riser pipe. Calculate friction loss through riser pipe down and
> > through sprinkler riser with an assumed flow entering the tank discharge
> pipe.
> > Eleveation and friction loss is what you are calculating.
> >
> > What about doing a flow test from the base of the riser?
> >
> > Arthur Tiroly
> > ATCO Fire Protection Design
> > Tiroly and Associates
> > 216-621-8899
> > 216-570-7030 Cell
> > WWW.ATCOfirepro.com
> >
> >
> > -----Original Message-----
> > From: [email protected]
> > [mailto:[email protected]] On Behalf Of Todd
> > Williams
> > Sent: Wednesday, June 16, 2010 7:17 AM
> > To: [email protected]
> > Subject: Re: Gravity Tanks
> >
> > I appreciate everybody's input. What about this?
> > Calculate the flow rate discharging at the bottom of the tank at the
> > pressure due to the elevation of the water in the tank. I found a
> > website that apparently will do that,
> > http://www.efunda.com/formulae/fluids/draining_tank.cfm#calc.
> > The static and residual pressures will be close to the same but will
> > decrease over time with the drop in water elevation. You could even
> > make the assumption on a residual pressure based on elevation after 1
> > minute of discharge and it would be conservative. So now you have a
> > static, residual and flow at the tank discharge. Then you could run it
> > through the piping down through the building (in this case) as you would
> any water supply.
> >
> >
> >
> >
> >
> > At 10:18 PM 6/15/2010, you wrote:
> >>I think Ralphy has it right. The empty tank level is the worst case
> >>pressure condition and in the big picture the falling tank head is
> >>nothing compared to 28 floors of head unless the tank height is a few
> >>sizes bigger than King Kong. A surprising calculation to make might be
> >>the tank stored gallons divided by the system gpm.
> >>
> >>On Jun 15, 2010, at 2:40 PM, Ralphy Henderson wrote:
> >>
> >> > Couldn't you also do this:
> >> >
> >> > For assumption sake let's say 1st floor is light hazard and we're
> >> > anticipating we're going to need 400 gpm. Plot out the static
> >> > pressure of the tank (at the empty level) over zero gpm then
> >> > calculate our friction losses through the main from the water tank
> >> > down to the first floor based upon our anticipated 400 gpm and
> >> > subtract that from our static to get our residual pressure. Plot
> >> > out the residual pressure over 400 gpm and we now have a standard
> >> > water supply curve that can be used to determine other pressures at
> >> > available flows.
> >> >
> >> > --- On Tue, 6/15/10, Brad <[email protected]> wrote:
> >> >
> >> > From: Brad <[email protected]>
> >> > Subject: RE: Gravity Tanks
> >> > To: "'Matt Grise'" <[email protected]>,
> >> > [email protected]
> >> > Date: Tuesday, June 15, 2010, 5:44 PM
> >> >
> >> > For turbulent (sprinkler) flows, friction loss is proportional to
> >> > the square of the velocity
> >> >
> >> > -----Original Message-----
> >> > From: Matt Grise [mailto:[email protected]]
> >> > Sent: Tuesday, June 15, 2010 12:41 PM
> >> > To: '[email protected]'; '[email protected]'
> >> > Subject: RE: Gravity Tanks
> >> >
> >> > Don't forget friction in the pipes!
> >> >
> >> > Matt Grisé PE*, LEED AP
> >> > Sales Engineer
> >> > Alliance Fire Protection
> >> > *Licensed in KS & MO
> >> >
> >> > 913.888.0647 ph
> >> > 913.888.0618 f
> >> > 913.927.0222 cell
> >> > www. AFPsprink.com
> >> >
> >> >
> >> > -----Original Message-----
> >> > From: [email protected]
> >> > [mailto:[email protected]] On Behalf Of Brad
> >> > Sent: Tuesday, June 15, 2010 12:39 PM
> >> > To: [email protected]; [email protected]
> >> > Subject: RE: Gravity Tanks
> >> >
> >> > i.e., if the water level is 280 feet 'above your head', then h=280
> >> > ft, v=134 ft/sec (same as the Law of Falling Bodies- if you were
> >> > dropped from 280 ft, you would be going 134 ft/sec when you hit the
> >> > ground).
> >> > ft/sec*ft^2=ft^3/sec. If the flow is coming out of 4" pipe, ft^2=.
> >> > 09----
> >> > *134= 12 * 7.48= 90---- * 60= 5400 GPM. As the level 'above your head'
> >> > drops, so does the velocity, so either use calculus, or call h the
> >> > bottom of the tank, like I would have to do. It still seems like
> >> > magic to me that by just using feet and seconds, given the rated
> >> > psi and rpm ONLY, of a fire pump, I can calculate the diameter of
> >> > the impeller (v=2*pi*r*f). It seems like magic bcoz for 15 years I
> >> > tried to learn sprinkler calcs after the PEs had simplified it
> >> > enough for me by factoring gravity out of the formulas.
> >> >
> >> > -----Original Message-----
> >> > From: Brad [mailto:[email protected]]
> >> > Sent: Tuesday, June 15, 2010 8:30 AM
> >> > To: [email protected]
> >> > Subject: RE: Gravity Tanks
> >> >
> >> > mgh=.5mv^2
> >> > m is the same on both sides so
> >> > v= sq root 2gh
> >> > h= v^2/2g
> >> > first thing is forget about gallons, minutes, and psi- use feet and
> >> > seconds:
> >> > ft, ft^2, ft^3, sec, sec^2. ft/sec=(ft^3/sec)/ft^2)
> >> > g=32.2 ft/sec^2 (if this project is on the earth). 7.48 gal/ft^3.
> >> > water
> >> > weighs 62.4 lbs/ft^3.
> >> >
> >> > -----Original Message-----
> >> > From: Todd Williams [mailto:[email protected]]
> >> > Sent: Tuesday, June 15, 2010 5:11 AM
> >> > To: [email protected]
> >> > Subject: Gravity Tanks
> >> >
> >> > Was there a thread on calculating flow from a gravity tanks a while
> >> > back? I couldn't find it. I have to do a calculation on the first
> >> > floor of a building fed from a gravity tank on the 28th floor
> >> >
> >> > Todd G. Williams, PE
> >> > Fire Protection Design/Consulting
> >> > Stonington, CT
> >> > 860.535.2080
> >> > www.fpdc.com
> >> >
> >> > _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > For Technical Assistance, send an email to:
> >> > [email protected]
> >> >
> >> > To Unsubscribe, send an email
> >> > to:[email protected]<to%[email protected]>
> >> > (Put the word unsubscribe in the subject field)
> >> >
> >> > _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > For Technical Assistance, send an email to:
> >> > [email protected]
> >> >
> >> > To Unsubscribe, send an email
> >> > to:[email protected]<to%[email protected]>
> >> > (Put the word unsubscribe in the subject field)
> >> >
> >> > _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > For Technical Assistance, send an email to:
> >> > [email protected]
> >> >
> >> > To Unsubscribe, send an email
> >> > to:[email protected]<to%[email protected]>
> >> > (Put the word unsubscribe in the subject field)
> >> >
> >> > _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > For Technical Assistance, send an email to:
> >> > [email protected]
> >> >
> >> > To Unsubscribe, send an email
> >> > to:[email protected]<to%[email protected]>
> >> > (Put the word unsubscribe in the subject field)
> >> >
> >> >
> >> >
> >> >
> >> > _______________________________________________
> >> > Sprinklerforum mailing list
> >> > [email protected]
> >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >> >
> >> > For Technical Assistance, send an email to:
> >> > [email protected]
> >> >
> >> > To Unsubscribe, send an email
> >> > to:[email protected]<to%[email protected]>
> >> > (Put the word unsubscribe in the subject field)
> >>
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email
> >>to:[email protected]<to%[email protected]>
> >>(Put the word unsubscribe in the subject field)
> >
> > Todd G. Williams, PE
> > Fire Protection Design/Consulting
> > Stonington, CT
> > 860.535.2080
> > www.fpdc.com
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to