The applicable codes should be noted on the cover sheet from the architect
after all we don't know what trade-offs were involved, if not contact the
E.O.R. for guidance.

On Tue, Jul 6, 2010 at 6:22 PM, Reed Roisum <[email protected]> wrote:

> IBC (ref. below 2006 ed.) allows 13R in Group I-1 if 4 stories or less.
>  Note exception...
>
> [F] , 903.2.5 Group I. An automatic sprinkler system shall be provided
> throughout buildings with a Group I fire area.
>        Exception: An automatic sprinkler system installed in accordance
> with Section 903.3.1.2 or 903.3.1.3 shall be   allowed in Group I-1
> facilities.
>
> [F] 903.3.1.2 NFPA 13R sprinkler systems. Where allowed in buildings of
> Group R, up to and including four stories in height, automatic sprinkler
> systems shall be installed throughout in accordance with NFPA 13R.
>
>
> Reed A. Roisum, CET
> Ulteig Engineers, Inc.
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Todd Williams
> Sent: Tuesday, July 06, 2010 4:52 PM
> To: [email protected]
> Subject: Re: Question regarding NFPA 13 vs. NFPA 13R
>
> Assisted living is an I-1 occupancy per ICC. Check you local code,
> but it would probably need to be a 13 system.
>
>
>
> At 05:46 PM 7/6/2010, you wrote:
> >For a single-story *assisted living* center, can 13R be used for the
> system
> >design ? If it can be designed per NFPA 13R, at what point would it need
> to
> >be protected per NFPA 13 ? I realize that 13R covers residential units up
> to
> >4 levels, but where this is an assisted living center, does this make a
> >difference ?
> >
> >Dan Adams
> >Designer
> >
> >Interwest Fire Protection, Inc.
> >404 Ironwood Drive
> >Salt Lake City, UT 84115
> >
> >Phone:     (801) 746-4040
> >Fax:         (801) 746-4043
> >[email protected]
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email 
> >to:[email protected]<to%[email protected]>
> >(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to