Roland,

I don't know that I am. Look at the requirements of of 903.2.8 for Group R.
It mentions that I need to comply with Section 903.3. Under section 903.3 -
13D is also an option. That doesn't mean that 13D is appropriate. It might
be, but it would depend on the building height/area and whether it is a
hotel, dorm, etc.

I contend that one must go back through the steps of identifying the
occupancy and work through the tradeoffs, heights, bldg area, etc. to get to
the appropriate section of Chapter 9. In this case the occupant load is part
of the driving factor of which way one should turn. And if that leads me
into the IRC... then great. But if not of to 13 / 13R land I go.

Best Regards,
Ken Holsopple





Why are you unnecessarily limiting yourself?  In other words, I  
disagree.  You are right that 308.2 kicks you to R-3 with fewer than 5  
persons but where does 903.2.6 say ANYTHING about using 903.3.1.3 in  
R-3. It says I-1 can use either 13R or 13D.  Granted this undoubtedly  
stemmed from many houses being converted to a small I-1 but it doesn't  
say anything about SIZE or construction type.  Now I assume that an  
AHJ could argue that the description of 903.3.1.3 would limit you to  
something similar to a one-and two family dwellings (which I've heard  
of houses with 13D systems just over 200,000 sf) but it certainly  
isn't very strong. I just now got it cleaned up that you actually have  
to inspect 13D systems in an I-1.

Now we'll wait for our AHJ code boys to elaborate.

Roland



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to