The Ohio IBC has allowed and encourages the use of residential sprinklers in
"I" occupancies. We have used the residential rules in 13 with 4 head calc
areas for many years. But attics etc are required for 100% sprinkler
coverage due to NFPA 13 requirements per IBC for the I occupancy.

ART
ATCO Fire Protection 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Sent: Wednesday, July 07, 2010 9:50 AM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

If this question is raised before the Arch finalizes the design, then the
common "I" areas (core) can be separated from the "R" (sleeping wings) with
a 2-hour wall, then 13 AND 13R apply, the overall cost is probably reduced,
and there is nothing wrong from a fire protection view.

-----Original Message-----
From: Daniel Adams [mailto:[email protected]]
Sent: Tuesday, July 06, 2010 4:47 PM
To: [email protected]
Subject: Question regarding NFPA 13 vs. NFPA 13R

For a single-story *assisted living* center, can 13R be used for the system
design ? If it can be designed per NFPA 13R, at what point would it need to
be protected per NFPA 13 ? I realize that 13R covers residential units up to
4 levels, but where this is an assisted living center, does this make a
difference ?

Dan Adams
Designer

Interwest Fire Protection, Inc.
404 Ironwood Drive
Salt Lake City, UT 84115

Phone:     (801) 746-4040
Fax:         (801) 746-4043
[email protected]
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to