The birth of the horizontal firewall. The architect's are rejoicing
here on Earth and in that private Hell reserved for them.

On Thu, Jul 8, 2010 at 12:58 PM, Roland Huggins
<[email protected]> wrote:
> I have preached that sermon many times and then the IBC changes the
> HORIZONTAL separation in the 2009 ed. from just parking garages on the
> lower levels to multiple types of occupancies.  Look for the soon
> released July issue of Sprinkler Age and the article by Phill Brown.
>
> Roland
>
> On Jul 7, 2010, at 10:46 AM, John Drucker wrote:
>
>> Brad,
>>
>> At issue is the notion of horizontal fire separation assembly being
>> the
>> same as a firewalls.
>>
>> There are two building separation concepts; 1) open space which allows
>> adjacent buildings to burn down without effecting another or 2) a fire
>> wall which allows adjacent buildings to burn down without effecting
>> another. In both cases the fire building is consumed without affecting
>> adjacent buildings.
>>
>> Obviously distance speaks for itself.
>>
>> The concept of a firewall delineating separate buildings is founded
>> on a
>> critical performance criteria ; "2006 IBC 702.1 FIRE WALL. A
>> fire-resistance-rated wall having protected openings, which restricts
>> the spread of fire and extends continuously from the foundation to or
>> through the roof, WITH SUFFICIENT STRUCTURAL STABILITY UNDER FIRE
>> CONDITIONS TO ALLOW COLLAPSE OF CONSTRUCTION ON EITHER SIDE without
>> collapse of the wall."
>>
>> So I ask, how does a horizontal fire assembly comply with this
>> critical
>> performance requirement ?.  The answer it doesn't.
>>
>> But to answer your question; "if a 2-hour wall between light hazard
>> and
>> something less than light hazard is called equivalent to a separate
>> building by the officials, then what do you rename it to?"  No need to
>> rename it since a 2 hour fall WALL qualifies the construction as two
>> separate buildings, so 13 in the non residential BUILDING and 13R is
>> the
>> residential BUILDING.
>>
>> John Drucker Jr CET
>> Fire Protection Subcode Official
>> Fire/Building/Electrical Inspector
>> Borough of Red Bank, NJ
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Brad
>> Sent: Wednesday, July 07, 2010 1:17 PM
>> To: 'John Drucker'; [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> John,
>> Good idea with the name change, but it would not satisfy those whom
>> want
>> to see nothing but sky surrounding nothing but residential--
>>
>> -----Original Message-----
>> From: John Drucker [mailto:[email protected]]
>> Sent: Wednesday, July 07, 2010 12:00 PM
>> To: [email protected]; [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> David,
>>
>> Exactly. Where all this "hybrid" stuff came from is beyond me. If you
>> have a building that qualifies as NFPA-13R then the system is a 13R
>> System.
>> NFPA-13R merely refers back to certain sections of 13 as a technical
>> reference not to imply that the system is somehow two systems, or a
>> 13R/13 system.
>>
>> Hypothetically if 13R was a standalone standard, i.e. copying and
>> pasteing the needed sections of 13, there wouldn't be any confusion
>> since users would never venture beyond 13R. But we all know that it
>> would increase the cost of the standard.
>>
>> One simple change would solve the mixed use conundrum;
>>
>> NFPA 13R: "Standard for the Installation of Sprinkler Systems in
>> RESIDENTIAL Occupancies up to and Including Four Stories in Height".
>>
>> To
>>
>> NFPA 13R: "Standard for the Installation of Sprinkler Systems in
>> RESIDENTIAL BUILDINGS up to and Including Four Stories in Height".
>>
>> John Drucker, CET
>> Fire Protection Subcode Official
>> Fire/Building/Electrical Inspector
>> Fire Marshals Office
>> Borough of Red Bank, NJ
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Autry,
>> David
>> Sent: Wednesday, July 07, 2010 10:23 AM
>> To: [email protected]; [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> I believe you can ONLY have a 13 building or a 13R building. You can't
>> mix
>> and match. One or the other.
>>
>>
>> David Autry
>> Plans Examiner
>> Nebraska State Fire Marshal's Office
>> 246 S. 14th Street
>> Lincoln, NE 68508
>> 402-471-9659
>> 402-471-3118 fax
>> www.sfm.ne.gov
>>
>> ** Note new email address: [email protected]
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Brad
>> Sent: Wednesday, July 07, 2010 9:20 AM
>> To: 'Art Tiroly'; [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> Residential heads and their calc rules are great where you can use
>> them.
>> You
>> would not be able to use them in say the physical therapy room,
>> whether
>> it
>> was 13 OR 13R. By true occupancy separation, you eliminate a lot of
>> bathroom
>> and closet heads, AND attic sprinklers.
>>
>>
>> -----Original Message-----
>> From: Art Tiroly [mailto:[email protected]]
>> Sent: Wednesday, July 07, 2010 9:02 AM
>> To: [email protected]; [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> The Ohio IBC has allowed and encourages the use of residential
>> sprinklers in
>> "I" occupancies. We have used the residential rules in 13 with 4 head
>> calc
>> areas for many years. But attics etc are required for 100% sprinkler
>> coverage due to NFPA 13 requirements per IBC for the I occupancy.
>>
>> ART
>> ATCO Fire Protection
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Brad
>> Sent: Wednesday, July 07, 2010 9:50 AM
>> To: [email protected]
>> Subject: RE: Question regarding NFPA 13 vs. NFPA 13R
>>
>> If this question is raised before the Arch finalizes the design, then
>> the
>> common "I" areas (core) can be separated from the "R" (sleeping wings)
>> with
>> a 2-hour wall, then 13 AND 13R apply, the overall cost is probably
>> reduced,
>> and there is nothing wrong from a fire protection view.
>>
>> -----Original Message-----
>> From: Daniel Adams [mailto:[email protected]]
>> Sent: Tuesday, July 06, 2010 4:47 PM
>> To: [email protected]
>> Subject: Question regarding NFPA 13 vs. NFPA 13R
>>
>> For a single-story *assisted living* center, can 13R be used for the
>> system
>> design ? If it can be designed per NFPA 13R, at what point would it
>> need
>> to
>> be protected per NFPA 13 ? I realize that 13R covers residential units
>> up to
>> 4 levels, but where this is an assisted living center, does this
>> make a
>> difference ?
>>
>> Dan Adams
>> Designer
>>
>> Interwest Fire Protection, Inc.
>> 404 Ironwood Drive
>> Salt Lake City, UT 84115
>>
>> Phone:     (801) 746-4040
>> Fax:         (801) 746-4043
>> [email protected]
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>>
>> CONFIDENTIAL AND PROPRIETARY:
>> This email message is intended only for the use of the individual or
>> entity to which it is addressed and may contain information that is
>> privileged and confidential, nor is it, unless specifically stated,
>> intended to be relied upon by any person or persons other than the
>> individual or entity named above and no warranties or
>> representations are made or intended to persons or entities not
>> named above.  If the reader is not the intended recipient, you are
>> hereby notified that any dissemination, distribution or copying of
>> this communication is strictly prohibited.  If you have received
>> this communication in error, please notify us immediately by
>> telephone, return this message to the address above and delete all
>> copies.  Thank you.
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to