I have reviewed the July 2010 TIA, so if you have a system that is in design
as we speak, if you use a 50% or less factory premixed solution, it is
acceptable?  The revised TIA, I think states that it is?  

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, July 09, 2010 8:53 AM
To: [email protected]
Subject: Re: Anti-Freeze

Below is the AFSA Alert to our members.

Additional testing is underway.  The NFPA and Fire Protection Research  
Foundation with the support of the sprinkler industry are moving  
incredibly fast.  There was a NFPA 13 TCC meeting on this subject  
earlier this year and the initial fire testing was completed in a few  
months indicating that a threat exists and that it appears to be  
restricted to a narrow scenario in he kitchen.  A second round of more  
detailed testing has been launched to determine definitively whether  
other locations may display similar consequences and what levels of  
concentrations are safe to be used.  These tests are underway and will  
also be completed in an amazingly short period of time (doing things  
in weeks instead of many months/years).

Since the Truckee fire has been mentioned, I'd like to say proceed  
with cation.  The Fire Department report says there is not enough  
information yet to draw any conclusions and the other report casually  
jumps to a broad conclusion.  There are some very interesting  
explosion patterns that should have been addressed as part of that  
conclusion.

Roland


AFSA Member  
Alert 
 
July 
  7, 2010



NFPA issues safety alert regarding antifreeze in residential sprinklers
On July 6, the National Fire Protection Association (NFPA) issued a  
safety alert recommending that residential fire sprinkler systems  
containing antifreeze should be drained and the antifreeze replaced  
with water. The alert follows a research study and an initial set of  
fire tests conducted after a fire incident raised concerns about  
antifreeze solutions in residential sprinkler systems. The incident  
involved a grease fire in a kitchen where a sprinkler with a high  
concentration of antifreeze deployed. The fire resulted in a single  
fatality and serious injury to another person.

AFSA has been and continues to follow these developments closely. We  
have urged that testing be conducted as quickly as possible, with the  
hope that the results and subsequent standards modifications can be  
made before cold weather arrives. AFSA is mindful that NFPA is  
obligated to take strong positions in support of life safety and we  
anticipated a moratorium on the use of antifreeze until testing was  
complete, but we were surprised by the recommendation to drain  
existing systems and replace antifreeze with water.

NFPA and the NFPA Research Foundation have put this issue as a top  
priority. They are moving very rapidly to complete testing on this  
issue. NFPA anticipates that testing will be complete, and Tentative  
Interim Amendments (TIAs) will be addressed prior to the Standards  
Council meeting in August. Their goal is to have recommendations or  
standards modifications prior to the arrival of the "cold season."

AFSA will continue to work closely with NFPA and keep you informed on  
future developments. Expect to hear more soon. Complete information is  
available from NFPA at www.nfpa.org/antifreeze/.


On Jul 7, 2010, at 11:25 AM, Autry, David wrote:

> Any comments about the Safety Alert from NFPA concerning anti-freeze  
> in residential fire sprinkler systems?
>
> I'm not comfortable requiring these systems to be drained down,  
> filled with water and no real fix in place.
>
> David Autry
> Plans Examiner
> Nebraska State Fire Marshal's Office

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to