Right.  I was addressing your comment about water supplies.   Either
way, whether you interpreted it as two "connected" buildings or two
"separate" buildings, it seems to me that a single fire service can feed
as many risers as you need, whether it comes from a pump or other
source.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Friday, July 09, 2010 3:13 PM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

2007 NFPA-13-8.2.4 Multiple buildings attached by canopies, covered
breezeways, common roofs, or a common wall(s) shall be permitted to be
supplied by a single fire sprinkler riser. The maximum system size shall
comply with 8.2.1.

John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Steve
Leyton
Sent: Friday, July 09, 2010 5:17 PM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

The standard essentially says that each building shall have its own
riser, notwithstanding the exceptions for running piping between
separate buildings with attached construction, such as covered walkways.
So if you had "two buildings" in the same structure, you would need two
risers, but you could meet the prescriptive requirements with a single
fire service entry.

Steve Leyton
Protection Design & Consulting
San Diego, CA




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of John
Drucker
Sent: Friday, July 09, 2010 11:52 AM
To: [email protected]
Subject: RE: Question regarding NFPA 13 vs. NFPA 13R

It will be interesting to see the water supply arrangements for these
"multiple buildings" including but not limited to the location of a fire
pump outside the building it serves in accordance with new section 2009
IBC 913.2.1.  If they're separate buildings then they have to be treated
accordingly. 

Hence why I pointed out the specific limitations of 2009 IBC 509.2 

John Drucker Jr CET
Fire Protection Subcode Official
Fire/Building/Electrical Inspector
Borough of Red Bank, NJ 

 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, July 09, 2010 1:09 PM
To: [email protected]
Subject: Re: Question regarding NFPA 13 vs. NFPA 13R

the point to be made is that the system type applies to the entire
building and a single structure can be multiple buildings.  This is not
a mixed use building but two buildings.  The BUILDING below the
horizontal separation is required to be protected per NFPA 13 as well as
being limited to Type 1A construction and only one level above grade
(can be many stories below grade). It is the building above that will be
in its entirety a 13R system.  It can be any type of construction but
the height is still measured to grade.


Roland

On Jul 8, 2010, at 6:27 PM, John Drucker wrote:

> Hmm really...............
>
> 2009 IBC 509.2 Horizontal building separation allowance. "A building 
> shall be considered as separate and distinct buildings FOR THE PURPOSE

> OF DETERMINING AREA LIMITATIONS, CONTINUITY OF FIRE WALLS, LIMITATION 
> OF NUMBER OF STORIES AND TYPE OF CONSTRUCTION where all of the 
> following conditions are met."
>
> So IBC 509.2 applies to the following criteria;
>
> 1. DETERMINING AREA LIMITATIONS
> 2. CONTINUITY OF FIRE WALLS
> 3. LIMITATION OF NUMBER OF STORIES
> 4. TYPE OF CONSTRUCTION
>
> No mention of fire sprinkler determinations in that section including 
> but not limited to the type of system or the grade height measurement 
> for the purposes of 13R application which begins at lowest FD vehicle 
> access not the pedestal. With that said in many cases the building 
> will exceed four stories in height negating the use of 13R.
>
> Also Mixed Use Exception 1 at 508.1 merely recognizes the fire 
> separation provisions of 509 as an alternate to 508.2, 508.3, or 
> 508.4., it's still a mixed use building. Continuing with 509.2 and the

> separation allowance criteria;
>
> 2009 509.2 Horizontal building separation allowance
>
> 6. The building BELOW THE HORIZONTAL ASSEMBLY SHALL BE PROTECTED 
> THROUGHOUT BY AN APPROVED AUTOMATIC SPRINKLER SYSTEM IN ACCORDANCE 
> WITH SECTION 903.3.1.1, (NFPA-13 not 13R !) and shall be permitted to 
> be any of the following occupancies:
>
> 6.1. Group S-2 parking garage used for the parking and storage of 
> private motor vehicles; 6.2. Multiple Group A, each with an occupant 
> load of less than 300; 6.3. Group B; 6.4. Group M; 6.5. Group R; and 
> 6.6. Uses incidental to the operation of the building (including entry

> lobbies, mechanical rooms, storage areas and similar uses).
>
> Frankly we just gained NFPA-13 sprinkler systems in any use below the 
> separation regardless of the use group ! The sprinkler requirement is 
> absolute, 6.1 thru 6.6 merely stipulate what uses are permitted below 
> the fire separation. It will be important for designers to check if a 
> 509 allowance is being proposed by the architect since sprinklers must

> be provided regardless of what section 903.2 stipulates.
>
> Some are playing a deadly game with the lives of firefighters by 
> utilizing the increased height allowances and then facilitating the 
> use of a sprinkler standard beyond its height criteria, a standard 
> which aqlso allows the interstitial spaces of trusses to go 
> unprotected.
>
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)


CONFIDENTIAL AND PROPRIETARY:
This email message is intended only for the use of the individual or
entity to which it is addressed and may contain information that is
privileged and confidential, nor is it, unless specifically stated,
intended to be relied upon by any person or persons other than the
individual or entity named above and no warranties or representations
are made or intended to persons or entities not named above.  If the
reader is not the intended recipient, you are hereby notified that any
dissemination, distribution or copying of this communication is strictly
prohibited.  If you have received this communication in error, please
notify us immediately by telephone, return this message to the address
above and delete all copies.  Thank you.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5266 (20100709) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5266 (20100709) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5266 (20100709) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
 

__________ Information from ESET NOD32 Antivirus, version of virus
signature database 5266 (20100709) __________

The message was checked by ESET NOD32 Antivirus.

http://www.eset.com
 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to