There are many instances where you NEED to use interstital heads- Tyco
CC1/CC2 or Viking COINs.
look at 13 and the mfr cutsheets. If in open wood trusses with gyp below,
you'll need draftcurtains, etc. 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Wednesday, July 28, 2010 5:09 PM
To: [email protected]
Subject: NFPA-13 & Wood Joist

People smarter than me.....
In a nut shell what are requirements of NFPA-13 and wood trusses? I know the
exceptions when the ceiling is within 6" of the bottom of the beam and such
but in general is it safe to assume "if it's wood it's wet"? The reason I
bring this up is because I'm working on a Rec. Center and one wing of the
building has Glu-Lam beams that are exposed except in a few areas where
there is a GWB ceiling. The engineer wants pendent heads in the ceilings and
upright heads above but only in the exit corridors, does that make any
sense?
 

Brian Harris

 

 


Design Engineer

 

First Defense Fire Protection
11957 Ramah Church Road
Huntersville NC 28078




[email protected]
www.firstdefensefire.com <outbind://80/www.firstdefensefire.com> 

 

Ph: 704.948.3506
Fax: 704.948.3507

 

 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to