It hasn't been 100 heads since the old UBC. IBC (2006) Section 903.4 has a 20 head exemption.
Robert J. Pielow, P.E. Fire Protection & Life Safety -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Larkin, Brian Sent: Tuesday, October 12, 2010 10:41 AM To: [email protected] Subject: No Fire Alram Control Panel for <100 Sprinklers Hi, I have observed several jobs recently where the contractor quoted code indicating that since there were less than 100 sprinklers, no central fire alarm control panel was required. Can anyone point me towards where this is documented in NFPA? We require connecting alarm contacts from our heat tracing control system to the control panel as required in NFPA-13 2010 and want to accommodate the smaller jobs. Kind regards, Brian ________________________________ This e-mail contains privileged and confidential information intended for the use of the addressees named above. If you are not the intended recipient of this e-mail, you are hereby notified that you must not disseminate, copy or take any action in respect of any information contained in it. If you have received this e-mail in error, please notify the sender immediately by e-mail and immediately destroy this e-mail and its attachments. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)