Brian,
Looking in the 2006 IFC, section 903.4 requires that the control valves
for any sprinkler system with 20 or more sprinklers must be electrically
supervised. I don't know how you could accomplish that without an FACP.
--
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]> e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
On 10/12/2010 8:41 AM, Larkin, Brian wrote:
Hi, I have observed several jobs recently where the contractor quoted code
indicating that since there were less than 100 sprinklers, no central fire
alarm control panel was required. Can anyone point me towards where this is
documented in NFPA? We require connecting alarm contacts from our heat tracing
control system to the control panel as required in NFPA-13 2010 and want to
accommodate the smaller jobs.
Kind regards, Brian
________________________________
This e-mail contains privileged and confidential information intended for the
use of the addressees named above. If you are not the intended recipient of
this e-mail, you are hereby notified that you must not disseminate, copy or
take any action in respect of any information contained in it. If you have
received this e-mail in error, please notify the sender immediately by e-mail
and immediately destroy this e-mail and its attachments.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)