The current code does not necessarily have to be legally enforceable. Some
building codes adopt the current codes while others specify a particular
year. When a particular edition is adopted, then that is the governing code.
Although a current code is more cutting edge, you could be faulted for
deviating from the governing code. Then again, you could also be faulted for
not keeping up with new tecnology. It is a case of damned if you did, and
damned if you don't. But between the two, I'd feel safer complying with the
governing code, and only complying with a current code, if it is more
stringent. Current codes generally reflect newer technology, studies and
research. But they are not necessarily always more stringent. For example,
remember the last time the density/area curves were revised? Parking garages
moved down from 0.16 to 0.15. Also, some obstruction rules have been
relaxed, over the years. In general, I'd say you will have a better chance
of defending yourself by complying with the governing code than the most
current code. Having said that, you also have to keep in mind that codes are
minimum standards, and there is nothing wrong (except for the owner's purse)
with exceeding the minimum standards.

Tony    

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Chris Cahill
Sent: November 3, 2010 10:51 AM
To: [email protected]
Subject: Older editions

Curious question, has there ever been a loss because of the use of an older
standard assuming it complied with any ed.?  So even with EQ were there
systems that had fires after earthquakes where the hangers failed and there
was a significant loss?  Or were the failures just hanger issues but no
fires?  And even then in EQ country is there anything requiring retrofit if
say it was built in '96?  If there was some history of failure would we
expect the newer standards to address in Ch. 1 retroactivity? 

There are plenty of losses due to closed/inadequate water.  Don't see that a
year issue.  There are a few noted as system not designed for the hazard.
But many of these the original system was complaint but the hazard changed
to the system never upgraded.  Or it was never right for the original
hazard. Again I don't see this as a year issue.

Chris Cahill  

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of David
Blackwell
Sent: Wednesday, November 03, 2010 10:58 AM
To: [email protected]
Subject: RE: Physical Science :)

Has anyone on the list gotten feedback from their insurance carrier
regarding using an old code [like the 1996 edition mentioned in the email
below]?  

I'm guessing they wouldn't like you designing to such an old code minimum
which had inadequate minimum standards that were later fixed in newer
editions of the code.  One glaring difference between 2010 & 1996 is in the
area of seismic protection which was upgraded after a couple of quakes in CA
demonstrated the code minimum requirements in that arena were insufficient.
If I were out in private practice I would be trying to design to the current
latest published editions so I didn't end up in court with a lawyer asking
me why I didn't use a more current edition...

 

David W. S. Blackwell, II, PE, CFI-I, CFPE Engineering
----------------------------------------------------------------
Office of State Fire Marshal
141 Monticello Trail
Columbia, SC 29203
Phone:  803.896.9833
Fax:  803.896.9806
Email:  [email protected]
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
---------------------------------------------------------------- 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, November 03, 2010 9:56 AM
To: [email protected]
Subject: RE: Physical Science :)

Sorry but when doing in-depth code analysis', there is no way you could find
every bit of information needed in a tabbed book versus doing a digital
search unless you have all the time in the world.  There is stuff buried in
these texts that is not in the index and unless you've stumbled across it
before and tagged it, you'd never find it.

Digital is here, now, not waiting for the next generation.

As far as the question concerning why NICET uses particular versions, it is
probably due to the amount of work involved with reworking a test.  Plus not
all jurisdictions jump on the new Standard immediately upon its publication.
I still have many jurisdictions using the 2002 NFPA 13 and had one earlier
in the year that was still on the 1996 version.  It would be a significant
task to develop a new test each time a new standard came out.

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, November 03, 2010 9:50 AM
To: [email protected]
Subject: RE: Physical Science :)

We old timers are used to paper, but the next generation will 
probably be much more geared to digital. Somehow NICET and others 
will need to adapt. Agencies are not going to continue print issues 
just for some open book testing agency. I agree that finding 
information in a tabbed text is still a lot quicker than a computer 
search. But perhaps testing agencies will have to provide computer 
access to certain reference materials as a part of the computer 
testing procedure.

Brian, as far as your question, I have wondered that as well. Perhaps 
they use a random number generator


At 09:21 AM 11/3/2010, you wrote:
>Here's a question for some of you veterans, how does NICET come up with
what
>year code will be on the test? I don't get why some of these codes are 2,3,
>and greater revisions behind the current one....
>
>Brian Harris
>FDFP Inc.
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of George
Church
>Sent: Wednesday, November 03, 2010 9:22 AM
>To: [email protected]
>Subject: RE: Physical Science :)
>
>Its not as easy as it sounds to change a 30-year old certification program
>as you might think.
>While it's a PIA to drag around all the reference materials, you must also
>appreciate the numerous concerns and integrity requirements and
restrictions
>faced by any testing agency. They need to prevent theft of test questions,
>they need to make sure you are using a hand calculator rather than allowing
>the possibility you'll run a calc program on a PC or programmable
>calculator, that you know where to look things up based on familiarity with
>the references rather than rely on a word search, etc.
>
>NICET is moving along with PC-based testing at readily accessible testing
>centers nationwide, with open scheduling and instant results. It's a large
>undertaking with substantial volunteer contribution to make it work. To
>speed it along, participate and donate your time and energy to the industry
>that puts food on your table.
>
>NICET is also facing some competition in the market which may or may not
>produce other streamlining of the process, but it is what it is and the
>integrity of the process demands checking and validating the changes, and
>that all takes time. Think of the 4 years +/- some of us have been involved
>in the process, lugging ourselves to Alexandria, and -not to sound like the
>proverbial schoolteacher, but I remember borrowing references from the
>Atlanta fire marshal so I had to spend Fri afternoon going downtown,
lugging
>the books to the car, getting familiar with them Fri night, and lugging
them
>to the exam and on Monday AM back to City Hall. It builds character and
>memories, like then-mayor Andrew Young getting in the elevator with me Fri
>and observing what a fun weekend I must be stocking up for :)
>
>glc
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of
>[email protected]
>Sent: Wednesday, November 03, 2010 8:56 AM
>To: [email protected]
>Subject: RE: Physical Science :)
>
>Really, all of our codes are now in digital format.  Much easier to search
>and cheaper for the company.  NICET needs to come into the 21st century
with
>this.  It's just crazy lugging 30-40 lbs of reference books to a test.  Had
>one test that was on 2nd floor and had to tote the load up the stairs.
Just
>plain ridiculous.
>
>Craig L. Prahl, CET
>Fire Protection
>CH2MHILL
>Lockwood Greene
>1500 International Drive
>Spartanburg, SC  29304-0491
>Direct - 864.599.4102
>Fax - 864.599.8439
>CH2MHILL Extension  74102
>[email protected]
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd
Williams
>Sent: Tuesday, November 02, 2010 7:08 PM
>To: [email protected]
>Subject: Re: Physical Science :)
>
>And don't forget to put index tabs on your references and take a
>dictionary with you.
>
>What are they going to do when al this stuff is on our iPads?
>
>
>At 06:39 PM 11/2/2010, you wrote:
> >Same here, Brian.  Of course I'm so old that when I took it with me
> >it was only one volume, not two.
> >--
> >
> >PARSLEY CONSULTING
> >
> >Ken Wagoner, SET
> >
> >760.745.6181 voice
> >
> >760.745.0537 fax
> >
> >[email protected] <mailto:[email protected]>e-mail
> >
> >www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
> >
> >
> >
> >
> >On 11/2/2010 2:46 PM, Jamie.seidl wrote:
> >>The fire protection handbook. It's all I used.
> >>
> >>Jamie
> >>Sent from my iPhone
> >>
> >>On Nov 2, 2010, at 5:08 PM, "Brian
> >>Harris"<[email protected]>  wrote:
> >>
> >>>Any recommendations for good reference material for the Physical
Science
> >>>portion of the Nicet test?
> >>>
> >>>
> >>>
> >>>Brian Harris
> >>>
> >>>First Defense Fire Protection
> >>>
> >>>11957 Ramah Church Road
> >>>
> >>>Huntersville, NC 28078
> >>>
> >>>Phone: 704.948.3506
> >>>
> >>>Fax: 704.948.3507
> >>>
> >>>Nicet # 128476
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>
> >>>=======
> >>>Email scanned by PC Tools - No viruses or spyware found.
> >>>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16210)
> >>>http://www.pctools.com/
> >>>=======
> >>>_______________________________________________
> >>>Sprinklerforum mailing list
> >>>[email protected]
> >>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>>
> >>>For Technical Assistance, send an email to: [email protected]
> >>>
> >>>To Unsubscribe, send an email
to:[email protected]
> >>>(Put the word unsubscribe in the subject field)
> >>_______________________________________________
> >>Sprinklerforum mailing list
> >>[email protected]
> >>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >>For Technical Assistance, send an email to: [email protected]
> >>
> >>To Unsubscribe, send an email
to:[email protected]
> >>(Put the word unsubscribe in the subject field)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>
>
>
>
>=======
>Email scanned by PC Tools - No viruses or spyware found.
>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>http://www.pctools.com/
>=======
>
>
>
>
>
>=======
>Email scanned by PC Tools - No viruses or spyware found.
>(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16220)
>http://www.pctools.com/
>=======
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to