Thanks Rich,

http://fire.nist.gov/bfrlpubs/fire98/art069.html

I hope this works- the link did but the pdf did not--

"sprinklers hurt the vents more than vice versa"-- I think sprinkler spray
in the ceiling jet cooled the fusing element on the auto vent so the vents
did not open more often than open vents kept sprinklers from opening.

Auto vents are supposed to improve visibility, therefore faster exiting, or,
more distance covered/time. 2009 IBC does not allow the increase in egress
distance with auto vents any more because of the above-- (vents were not
opening).


-----Original Message-----
From: Richardson, R [mailto:[email protected]] 
Sent: Friday, November 05, 2010 11:09 AM
To: [email protected]
Subject: RE: smoke vents for retrofit

I will be surprised if you find a definitive answer anywhere to this
question in a book.  Let me know if you do, I have been trying to get a
decision (long story) on this issue in existing storage buildings here for
years.

All depends on the "opinion" of the person with the most stripes sitting in
the chair at the time.

I think that the statement mentioned below "sprinklers hurt the vents more
than vice versa" though a significant factor with respect to cold smoke in
an atrium smoke exhaust situation, is not true with sprinklers and vents in
storage occupancies, but I have also been too busy read all the latest so...


Also, not so sure that vents in a storage have anything to do with exit
distance in modern codes.

Rich Richardson
Seattle Fire Department

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Thursday, November 04, 2010 14:40
To: [email protected]
Subject: RE: smoke vents for retrofit

Matt,
I don't know, Codes is too busy, (I have clocked out, but don't know much)
but one guy said occupancy change is like a new building, and that's what
you asked. NIST did some good studies of auto vent/sprinkler interaction,
you probably know-- if they have to be together, at least sprinklers hurt
vents more than vice versa. For a phenomenal, oops, I mean nominal fee, you
could get some timed egress analysis done-- here is the marketing pitch--
"it will take a lot of time and money, but there is no guarantee of success"

  
  
-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Thursday, November 04, 2010 3:25 PM
To: [email protected]
Subject: RE: smoke vents for retrofit

Matt,
I will ask the code people here in a little while, but my 1st thought is-
was any kind of life safety analysis done? I think some manual vents would
be required, but auto vents would be based on egress lengths.

-----Original Message-----
From: Matt Grise [mailto:[email protected]] 
Sent: Thursday, November 04, 2010 2:53 PM
To: '[email protected]'
Subject: smoke vents for retrofit

If an existing building is retrofit with an area/density system to protect
high piled storage, does it need to have smoke vents and draft curtains
added as described in the IFC, or is that just new construction?

I looked around in the IFC/IBC/IEBC books, but I could not find anything
that would exempt the vents and curtains. Does anyone recall any way to
avoid them (other than ESFR)?

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to