My son's fraternity house is huge- 1st Governor's Mansion in Kansas- 68
dudes and a house mother. On move-in day, I told one of the guys I am very
glad to see sprinklers everywhere- he said 'we don't throw footballs around
in here because if a sprinkler breaks they will all go off'. I set him
straight but maybe should not have. I wanted to say 'that little notched
wheel at the bottom spins when water comes out'.
BTW, my son told me 'We don't abbreviate the word fraternity any more than
we abbreviate the word Country'.

-----Original Message-----
From: George Church [mailto:[email protected]] 
Sent: Wednesday, November 10, 2010 12:18 PM
To: [email protected]
Subject: RE: QR sprinklers in R2 occupancy

So pledges should receive small souvenir bats and metal straps as their
welcome package, not balls, etc.

Seriously, good stuff Jim- Thanks!

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jim Davidson
Sent: Wednesday, November 10, 2010 1:06 PM
To: [email protected]
Subject: RE: QR sprinklers in R2 occupancy

There was a project in the Mid Atlantic region in which the Architect
specified "Institutional" QR heads in a "mid rise" student housing building.
Three days after the students moved in there was a fairly large water damage
claim resulting from damage to the "Institutional" sprinklers from the
students throwing around balls, etc. Needless to say it occurred on the top
floor level and flowed downhill. Institutional type sprinkler heads should
be used in the occupancy that they were designed for. 

The last frat house that we worked on the Owner wanted the pipe to be able
to support at least five times the weight of the water filled pipe plus 500
pounds and wanted the strongest head guard that is manufactured to be used
on all sprinkler heads in the frat house and wanted all pipe to be scheduled
40.   

Jim Davidson 
 
Davidson Associates
Fire Protection * Medical Gas * Code Consulting
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, November 10, 2010 10:01 AM
To: [email protected]
Subject: RE: QR sprinklers in R2 occupancy

Yep it is a frat house.  I am trying to convince the arch to go with the
concealed type res sprinklers.
The only place we would have to use semi-recessed is when throwing across
the 4/12 ceilings.
Thanks for the information.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Church
Sent: Wednesday, November 10, 2010 8:57 AM
To: [email protected]
Subject: RE: QR sprinklers in R2 occupancy

Correct. And if the total # of heads in a dwelling unit is 4, you can QR.
Finally, someone treating a fraternity commiserate with the exposure?
Or would concealed heads be enough protection from mechanical injury so you
could use the residential heads you should use?
Threat of someone hanging themselves?
Don't forget you'll need .1 for the QRs vrs .05.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Wednesday, November 10, 2010 8:28 AM
To: [email protected]
Subject: QR sprinklers in R2 occupancy

I have a R2 occupancy that is to be sprinklered per NFPA13R (07ed).  The
architect wants to use quick response institutional sprinklers.
It appears that per 6.7.7.1.3 I can use QR sprinklers inside the dwelling
unit only if it meets the definition of a compartment with no more than 4
sprinklers.  If the dwelling unit contains multiple rooms
(ie:
bathroom, kitchen, ect.) then this unit would not qualify because it is not
single compartment correct?  What if with all the compartments together
there would only be 4 sprinklers?
 
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
<http://www.designbuildfire.com/>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to