I say yes to below.

8.5.5.3.1 Sprinklers shall be installed under fixed obstructions
over 4 ft (1.2 m) wide such as ducts, decks, open grate
flooring, cutting tables, and overhead doors.

No to the CC, as the space is not combustible.

R/
Matt

 

 

Matthew J. Willis, CET
Automatic Fire Sprinklers
Norred Fire Systems L.L.C.
318-387-1134 Voice
318-816-1087 Mobile
318-387-1163 Facsimile
[email protected]
> >-----Original Message-----
> >From: [email protected] [mailto:sprinklerforum-
> >[email protected]] On Behalf Of A.P.Silva
> >Sent: Thursday, November 11, 2010 12:29 PM
> >To: [email protected]
> >Subject: RE: Paint spray booth
> >
> >Thanks, my thoughts are the same, but wanted to see how the rest
> >interpreted
> >the code, as it is a bit ambiguous.
> >
> >Another question on spray booths. This is a downdraft booth. The booth
> >floor
> >will be a open mesh steel grill, with a concrete air plenum below it. The
> >air from the booth will exhaust into the air plenum below floor level and
> >up
> >thru' an exhaust duct. My question is will the air plenum below the floor
> >level, have to be sprinklered, based on a open grate flooring, over 4
> >feet
> >wide? Or not sprinklered, based on over 70% open, open-grid ceiling?
> >
> >If required to be sprinklered, and the space is less than 3 feet high,
> >will
> >combustible concealed space sprinklers be required. The space is
> >non-combustible and the quick response CC heads are not listed for extra
> >hazard applications. Will that suffice to argue for using standard
> >sprinklers, although the spray pattern may not be optimal?
> >
> >Tony
> >
> >-----Original Message-----
> >From: [email protected]
> >[mailto:[email protected]] On Behalf Of Ron
> >Greenman
> >Sent: November 10, 2010 4:11 PM
> >To: [email protected]
> >Subject: Re: Paint spray booth
> >
> >One for all. The purpose is the same as a for a cooking line with water.
> >To
> >shut down the sub-system for head changing (scheduled maintenance or
> >emergency maintenance) without needing to shut down and drain the entire
> >system. You could possibly get push back from an AHJ wanting one per hood
> >but I'd argue my point and then if that failed argue to avoid a separate
> >one
> >for mixing room.
> >
> >On Wed, Nov 10, 2010 at 2:54 PM, A.P.Silva <[email protected]> wrote:
> >> NFPA 13, 2007 section 21.4.1.5 : The sprinkler system for each spray
> >> area and mixing room shall be controlled by a separate, listed
> >> indicating valve(s), operable from the floor.
> >>
> >> I have two spray booths and a mixing booth side by side. Can one valve
> >> supply the three booths or are three valves required, one per booth?
> >>
> >> Tony
> >>
> >> _______________________________________________
> >> Sprinklerforum mailing list
> >> [email protected]
> >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >>
> >> For Technical Assistance, send an email to: [email protected]
> >>
> >> To Unsubscribe, send an email
> >> to:[email protected]
> >> (Put the word unsubscribe in the subject field)
> >>
> >
> >
> >
> >--
> >Ron Greenman
> >Instructor
> >Fire Protection Engineering Technology
> >Bates Technical College
> >1101 So. Yakima Ave.
> >Tacoma, WA 98405
> >
> >[email protected]
> >
> >http://www.bates.ctc.edu/fireprotection/
> >
> >253.680.7346
> >253.576.9700 (cell)
> >
> >Member:
> >AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
> >
> >They are happy men whose natures sort with their vocations. -Francis
> >Bacon,
> >essayist, philosopher, and statesman (1561-1626)
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
> >
> >No virus found in this incoming message.
> >Checked by AVG - www.avg.com
> >Version: 9.0.869 / Virus Database: 271.1.1/3246 - Release Date: 11/11/10
> >01:34:00

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to