And I concur with all. Yes to sprinklered and no to CC heads but not
because it is non-combustible, but because it is part of the
duct/plenum assembly.

On Thu, Nov 11, 2010 at 11:17 AM,  <[email protected]> wrote:
> The spray area needs to be sprinklered.  The spray area is the booth and
> the entire run of  duct work (plenum).
>
> John Hoffman P.E. | Fire Protection Engineer | Facility Engineering
> Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear
> Security Administration's Kansas City Plant | Operated by Honeywell FM&T |
> 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 |
> [email protected]
>
>
>
>  From:       "A.P.Silva" <[email protected]>
>
>  To:         <[email protected]>
>
>  Date:       11/11/2010 12:28 PM
>
>  Subject:    RE: Paint spray booth
>
>  Sent by:    [email protected]
>
>
>
>
>
>
> Thanks, my thoughts are the same, but wanted to see how the rest
> interpreted
> the code, as it is a bit ambiguous.
>
> Another question on spray booths. This is a downdraft booth. The booth
> floor
> will be a open mesh steel grill, with a concrete air plenum below it. The
> air from the booth will exhaust into the air plenum below floor level and
> up
> thru' an exhaust duct. My question is will the air plenum below the floor
> level, have to be sprinklered, based on a open grate flooring, over 4 feet
> wide? Or not sprinklered, based on over 70% open, open-grid ceiling?
>
> If required to be sprinklered, and the space is less than 3 feet high, will
> combustible concealed space sprinklers be required. The space is
> non-combustible and the quick response CC heads are not listed for extra
> hazard applications. Will that suffice to argue for using standard
> sprinklers, although the spray pattern may not be optimal?
>
> Tony
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: November 10, 2010 4:11 PM
> To: [email protected]
> Subject: Re: Paint spray booth
>
> One for all. The purpose is the same as a for a cooking line with water. To
> shut down the sub-system for head changing (scheduled maintenance or
> emergency maintenance) without needing to shut down and drain the entire
> system. You could possibly get push back from an AHJ wanting one per hood
> but I'd argue my point and then if that failed argue to avoid a separate
> one
> for mixing room.
>
> On Wed, Nov 10, 2010 at 2:54 PM, A.P.Silva <[email protected]> wrote:
>> NFPA 13, 2007 section 21.4.1.5 : The sprinkler system for each spray
>> area and mixing room shall be controlled by a separate, listed
>> indicating valve(s), operable from the floor.
>>
>> I have two spray booths and a mixing booth side by side. Can one valve
>> supply the three booths or are three valves required, one per booth?
>>
>> Tony
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis Bacon,
> essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to