As well, CCSS sprinklers are not listed for this type of protection.  Light 
hazard only.

BK

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Thursday, November 11, 2010 12:22 PM
To: [email protected]
Subject: Re: Paint spray booth

And I concur with all. Yes to sprinklered and no to CC heads but not because it 
is non-combustible, but because it is part of the duct/plenum assembly.

On Thu, Nov 11, 2010 at 11:17 AM,  <[email protected]> wrote:
> The spray area needs to be sprinklered.  The spray area is the booth 
> and the entire run of  duct work (plenum).
>
> John Hoffman P.E. | Fire Protection Engineer | Facility Engineering 
> Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear 
> Security Administration's Kansas City Plant | Operated by Honeywell 
> FM&T |
> 2000 E. 95th St | Kansas City, MO  64131 | ph 816-997-7213 | 
> [email protected]
>
>
>
>  From:       "A.P.Silva" <[email protected]>
>
>  To:         <[email protected]>
>
>  Date:       11/11/2010 12:28 PM
>
>  Subject:    RE: Paint spray booth
>
>  Sent by:    [email protected]
>
>
>
>
>
>
> Thanks, my thoughts are the same, but wanted to see how the rest 
> interpreted the code, as it is a bit ambiguous.
>
> Another question on spray booths. This is a downdraft booth. The booth 
> floor will be a open mesh steel grill, with a concrete air plenum 
> below it. The air from the booth will exhaust into the air plenum 
> below floor level and up thru' an exhaust duct. My question is will 
> the air plenum below the floor level, have to be sprinklered, based on 
> a open grate flooring, over 4 feet wide? Or not sprinklered, based on 
> over 70% open, open-grid ceiling?
>
> If required to be sprinklered, and the space is less than 3 feet high, 
> will combustible concealed space sprinklers be required. The space is 
> non-combustible and the quick response CC heads are not listed for 
> extra hazard applications. Will that suffice to argue for using 
> standard sprinklers, although the spray pattern may not be optimal?
>
> Tony
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron 
> Greenman
> Sent: November 10, 2010 4:11 PM
> To: [email protected]
> Subject: Re: Paint spray booth
>
> One for all. The purpose is the same as a for a cooking line with 
> water. To shut down the sub-system for head changing (scheduled 
> maintenance or emergency maintenance) without needing to shut down and 
> drain the entire system. You could possibly get push back from an AHJ 
> wanting one per hood but I'd argue my point and then if that failed 
> argue to avoid a separate one for mixing room.
>
> On Wed, Nov 10, 2010 at 2:54 PM, A.P.Silva <[email protected]> wrote:
>> NFPA 13, 2007 section 21.4.1.5 : The sprinkler system for each spray 
>> area and mixing room shall be controlled by a separate, listed 
>> indicating valve(s), operable from the floor.
>>
>> I have two spray booths and a mixing booth side by side. Can one 
>> valve supply the three booths or are three valves required, one per booth?
>>
>> Tony
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>> to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to