Hang the lights above the center of the aisles and ignore them. 
Mark at Aero

----- Original Message -----
From: [email protected] 
<[email protected]>
To: [email protected] <[email protected]>
Sent: Thu Nov 18 08:22:37 2010
Subject: ESFR's & Lights

I've read through the archives and found similar post regarding ESFR heads
and the obstructions caused by lights. Would it be safe to say in a
situation where the owner wants to install 2'x4' suspended lights in rows in
a warehouse that is protected by and ESFR system that either (A) the lights
need to be installed above the sprinklers or (B) additional heads will have
to be added under the lights? Thanks!

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506