I've read through the archives and found similar post regarding ESFR heads
and the obstructions caused by lights. Would it be safe to say in a
situation where the owner wants to install 2'x4' suspended lights in rows in
a warehouse that is protected by and ESFR system that either (A) the lights
need to be installed above the sprinklers or (B) additional heads will have
to be added under the lights? Thanks!

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16330)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to