Not sure if this falls under your situation, but FM states Continuous
obstructions below sprinklers wider than 12" and no wider than 24": locate
sprinkler deflector at least 24" horizontally from the nearest edge of the
obstruction.

Thanks,
Gregg Fontes
Cen-Cal Fire Systems, Inc.
209-334-9119

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron.Fletcher
Sent: Thursday, November 18, 2010 7:52 AM
To: [email protected]
Subject: RE: ESFR's & Lights

Centered between two rows of heads high enough to comply with 8.12.5.1.1 is
always safe. Or I would add more than 3 ft down but that is my opinion only.
If things more than 3 ft down mattered the storage would be an obstruction?

Ron Fletcher
Aero Automatic
Phoenix, AZ

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, November 18, 2010 8:44 AM
To: [email protected]
Subject: RE: ESFR's & Lights

Ron-
I guess my question would be then where could you place them that they
wouldn't be an obstruction?

Brian Harris
FDFP Inc.
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron.Fletcher
Sent: Thursday, November 18, 2010 10:25 AM
To: [email protected]
Subject: RE: ESFR's & Lights

Typically we would work with the owner and electrician to locate the lights
where they are not an obstruction. Unless of course they are storing lights.
Lights could be stored to within 3 ft of the ESFR's so is a row of light
fixtures more than 3 ft down an obstruction?   

Ron Fletcher
Aero Automatic
Phoenix, AZ 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Thursday, November 18, 2010 7:23 AM
To: [email protected]
Subject: ESFR's & Lights

I've read through the archives and found similar post regarding ESFR heads
and the obstructions caused by lights. Would it be safe to say in a
situation where the owner wants to install 2'x4' suspended lights in rows in
a warehouse that is protected by and ESFR system that either (A) the lights
need to be installed above the sprinklers or (B) additional heads will have
to be added under the lights? Thanks!

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16330)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16330)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16330)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to