To be considered non-combustible, the material must be ASTM E 136 compliant, 
see 3.3.12 in the definitions section.

Duane Johnson, PE
Program Manager
Division of the Fire Marshal (Support Contractor)
Office of Research Services 
National Institutes of Health 
301-496-0487

"Protecting Science - One Sprinkler at a Time"


-----Original Message-----
From: Todd Williams [mailto:[email protected]] 
Sent: Tuesday, December 14, 2010 2:51 PM
To: [email protected]
Subject: RE: partial egress system

The stairs are pressure treated wood (actually visited the site yesterday)


At 02:10 PM 12/14/2010, you wrote:
>Sorry, not sure where this thread ended but here is a reference to consider:
>
>8.15.3.2.4    Sprinklers shall be permitted to be omitted from 
>exterior stair towers when the exterior walls of the stair tower are 
>at least 50 percent open and when the stair tower is entirely of 
>noncombustible construction.
>
>
>Duane Johnson, PE
>Program Manager
>Division of the Fire Marshal (Support Contractor)
>Office of Research Services
>National Institutes of Health
>301-496-0487
>
>"Protecting Science - One Sprinkler at a Time"
>
>
>At 07:51 AM 12/9/2010, you wrote:
> >I have an AHJ that is requesting a partial system in an existing 8
> >family apartment building (two story). He wants sprinklers by all
> >windows and doors near exterior fire escapes and sprinklers under
> >the platforms of the FE's. There are no sprinklers currently in the
> >building. When I asked him for the Code reference, he said "You're
> >the design professional, you tell me." The CT Fire Safety Code is a
> >bastardized version of the IFC and NFPA 101 and I can't find any
> >reference to it. Anybody out there heard of such a thing?
> >
> >Todd G. Williams, PE
> >Fire Protection Design/Consulting
> >Stonington, CT
> >860.535.2080
> >www.fpdc.com
> >
> >_______________________________________________
> >Sprinklerforum mailing list
> >[email protected]
> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> >For Technical Assistance, send an email to: [email protected]
> >
> >To Unsubscribe, send an email to:[email protected]
> >(Put the word unsubscribe in the subject field)
>
>Vince Sabolik
>Christi Fire Protection, Inc.
>11351 Pearl Road
>Strongsville, Ohio 44136
>
>T 440 572-7730  F 440 572-7719  Email:
><mailto:[email protected]>[email protected]
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to