NFPA 13 (2002) section 9.2.3.4.3 discusses hanger spacing deviations for piping with maximum pressure exceeding 100 psi as being different from spacing with pressures less than that. If the fire department hooks up to the FDC with 150 psi pressure, would that be the valve used for determining the maximum pressure? If that is the case, when would the lesser value be used?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to