13 pretty much ignores FDC's except to say they are magical connections that 
somehow allow the fire department to "supplement" pressure without adding flow.

Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, January 05, 2011 5:16 AM
To: [email protected]
Subject: Hanger spacing - 100 psi

NFPA 13 (2002) section 9.2.3.4.3 discusses hanger spacing deviations 
for piping  with maximum pressure exceeding 100 psi as being 
different from spacing with pressures less than that. If the fire 
department hooks up to the FDC with 150 psi pressure, would that be 
the valve used for determining the maximum pressure? If that is the 
case, when would the lesser value be used?

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com