Lets start the clarification by saying that this is not about hangar
spacing but the unsupported length from the hangar to the last
sprinkler. Your ending question is a pretty good clue. It also helps
that 9.2.3.4.3.1 says "applied other than through the fire dept
connection". Are you working at 3 AM again?
Roland
On Jan 5, 2011, at 4:15 AM, Todd Williams wrote:
NFPA 13 (2002) section 9.2.3.4.3 discusses hanger spacing deviations
for piping with maximum pressure exceeding 100 psi as being
different from spacing with pressures less than that. If the fire
department hooks up to the FDC with 150 psi pressure, would that be
the valve used for determining the maximum pressure? If that is the
case, when would the lesser value be used?
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)