My guess would be 2009 IBC 903.4.2. You'll note the requirement for activation on waterflow EQUIVALENT TO the flow of a single sprinkler. It doesn't say where this flow originates so I would assume it could be between the pump and the risers. I don't think the pump run signal is the same because this should be a supervisory condition and may not indicate any flow at all. This may be your AHJ's hook on which his/her opinion hangs.
Bill Brooks William N. Brooks, P.E. Brooks Fire Protection Engineering Inc. 372 Wilett Drive Severna Park, MD 21146-1904 410-544-3620 410-544-3032 FAX 412-400-6528 Cell -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom Sent: Saturday, January 08, 2011 3:09 PM To: [email protected] Subject: RE: Main Flow Switch AHJ Requesting "Main Flow Switch" between fire pump and risers. In word searching NFPA 13, 20, 101 and 72 (2007)I can find no definition of a "Main Flow Switch" nor any requirement for one. The pump run signal will provide the same alarm as the "Main Flow" but the AHJ says it's in the code. Where? He says find it! Any help out there?? Thom _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)