Todd,

Since your building is less than 3 stories in height this would not be 
applicable, but it does require sprinklers ONLY at exits and corridors.

>From the International Existing Building Code, 2006 edition:

704.2.2 Groups A, E, F-1, H, I, M, R-1, R-2, R-4, S-1 and S-2. In buildings 
with occupancies in Groups A, E, F-1, H, I, M, R- 1, R-2, R-4, S-1, and S-2, 
work areas that include exits or corridors shared by more than one tenant or 
that serve an occupant load greater than 30 shall be provided with automatic 
sprinkler protection where all of the following conditions occur: 

1. The work area is required to be provided with automatic sprinkler protection 
in accordance with the International Building Code as applicable to new 
construction; 

2. The work area exceeds 50 percent of the floor area; and 

3. The building has sufficient municipal water supply for design of a fire 
sprinkler system available to the floor without installation of a new fire 
pump. 

Exception: Work areas in Group R occupancies three stories or less in height. 


Jack Fairchild, CFPS  |  Manager of Fire Protection and Life Safety  
|  Ballinger  |  v 215.446.0596 |   f  215.446.0597  |  833 Chestnut Street  
Suite 1400    Philadelphia, PA   19107  |  www.ballinger-ae.com

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, December 14, 2010 3:10 PM
To: [email protected]
Subject: RE: partial egress system

FYI - The CT Fire Safety Code is printed on 8.5 x 11 paper, but the 
2009 supplement is printed on 8.5 x 14 - so you can't put the update 
with the Code. Tragically consistent.


At 02:50 PM 12/14/2010, you wrote:
>The stairs are pressure treated wood (actually visited the site yesterday)
>
>
>At 02:10 PM 12/14/2010, you wrote:
>>Sorry, not sure where this thread ended but here is a reference to consider:
>>
>>8.15.3.2.4    Sprinklers shall be permitted to be omitted from 
>>exterior stair towers when the exterior walls of the stair tower 
>>are at least 50 percent open and when the stair tower is entirely 
>>of noncombustible construction.
>>
>>
>>Duane Johnson, PE
>>Program Manager
>>Division of the Fire Marshal (Support Contractor)
>>Office of Research Services
>>National Institutes of Health
>>301-496-0487
>>
>>"Protecting Science - One Sprinkler at a Time"
>>
>>
>>At 07:51 AM 12/9/2010, you wrote:
>> >I have an AHJ that is requesting a partial system in an existing 8
>> >family apartment building (two story). He wants sprinklers by all
>> >windows and doors near exterior fire escapes and sprinklers under
>> >the platforms of the FE's. There are no sprinklers currently in the
>> >building. When I asked him for the Code reference, he said "You're
>> >the design professional, you tell me." The CT Fire Safety Code is a
>> >bastardized version of the IFC and NFPA 101 and I can't find any
>> >reference to it. Anybody out there heard of such a thing?
>> >
>> >Todd G. Williams, PE
>> >Fire Protection Design/Consulting
>> >Stonington, CT
>> >860.535.2080
>> >www.fpdc.com
>> >
>> >_______________________________________________
>> >Sprinklerforum mailing list
>> >[email protected]
>> >http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> >For Technical Assistance, send an email to: [email protected]
>> >
>> >To Unsubscribe, send an email to:[email protected]
>> >(Put the word unsubscribe in the subject field)
>>
>>Vince Sabolik
>>Christi Fire Protection, Inc.
>>11351 Pearl Road
>>Strongsville, Ohio 44136
>>
>>T 440 572-7730  F 440 572-7719  Email:
>><mailto:[email protected]>[email protected]
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to