Intake plenum? Do you mean exhaust plenum?

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: January 10, 2011 6:53 PM
To: [email protected]
Subject: Re: sprinklers in duct

 I had to flow heads in the pit, intake plenum, exhaust duct, etc. except
the mixing room when i used to design the spray booths for Blowtherm. That's
what the A.H.J. usually required. I was able to get a compromise with them
allowing me to use different orifice sizes in different areas of the booth
so as not to have to install a 6" riser for all the overage.


George Medina Jr. 
Monterey Park, Ca

-----Original Message-----
From: Ron Greenman <[email protected]>
To: sprinklerforum <[email protected]>
Sent: Mon, Jan 10, 2011 2:05 pm
Subject: Re: sprinklers in duct


The duct or the spray booth? just figure all.
On Mon, Jan 10, 2011 at 1:46 PM, Todd Williams <[email protected]> wrote:
 OK, but there are two items that I have heard of, but can't find a
reference
 for: 1) the requirement for a sprinkler within 3 ft of the duct passing to
the outside, and 2) using pendent sprinklers in the vertical position on
vertical runs of duct.

 Also, there is the nebulous statement "the water supply shall be sufficient
to supply all sprinklers likely to open in any one fire incident..." How
does one go about determining the number of sprinklers likely to open that
would be reasonable and satisfy the AHJ as well as the attorney for the
plaintiff?



 At 03:49 PM 1/10/2011, you wrote:
>
> Or chapter 21 in NFPA 13
>
> Teresa M. King, S.E.T.
> Design Manager
> Front Range Fire Protection, Inc.
> 4007 S. Lincoln Avenue, Suite 460
> Loveland, CO  80537
> ph. (970) 663-3310
> fax (970) 663-7331
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dale 
> Wingard
> Sent: Monday, January 10, 2011 1:44 PM
> To: [email protected]
> Subject: RE: sprinklers in duct
>
> Try NFPA 33.  It is for Spray Application Using Flammables.
>
> Dale F. Wingard, SET
> Design Manager
> Triple "A" Fire Protection, Inc.
> 251.649.2034
> [email protected]
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Todd 
> Williams
> Sent: Monday, January 10, 2011 2:38 PM
> To: [email protected]
> Subject: sprinklers in duct
>
> I am doing a system for a spray booth and the associated exhaust 
> ducts. I can't seem to find the section of the NFPA standards that 
> references this. NFPA 91 says provide sprinkler protection without any 
> further guidance. NFPA 13 chapter 7 talks about cooking equipment and 
> it's ductwork, but doesn't give many specifics. Seems to me there is 
> something about having sprinklers within 3 ft of where the duct exits 
> the building, but I can't find it. Anybody know where this stuff is 
> off the top of their head?
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)

 Todd G. Williams, PE
 Fire Protection Design/Consulting
 Stonington, CT
 860.535.2080
 www.fpdc.com

 _______________________________________________
 Sprinklerforum mailing list
 [email protected]
 http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

 For Technical Assistance, send an email to: [email protected]

 To Unsubscribe, send an email to:[email protected]
 (Put the word unsubscribe in the subject field)


--
on Greenman
nstructor
ire Protection Engineering Technology
ates Technical College
101 So. Yakima Ave.
acoma, WA 98405
[email protected]
http://www.bates.ctc.edu/fireprotection/
253.680.7346
53.576.9700 (cell)
Member:
FSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC They are happy
men whose natures sort with their vocations. -Francis acon, essayist,
philosopher, and statesman (1561-1626)
______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected] To
Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to