consider the argument:
  the BFV failed because the disk was plated.
  if the sole source of corrosion was simply the plating,
  then pipe plated with zinc would self-corrode as well,
    in which case, it is a sham and a shameful marketing scheme...

    but plating in and of itself is not the cause.
    plating is the potential, or if you will...
    plating is the stored energy waiting to be turned into
    what a battery working off chemical electroPOTENTIALS
    from the different metals.
    (think of a ball sitting on a hill
     capable of rolling down, but won't until it is pushed.
     Eddy may go;  but plating wont -- at least until the base metal shows).

    something has to break the plating,
    in order to complete the circuit and set up the galvanic cell.

    if the plating is thin, the integrity can then
    be easily compromised.  If the plating is thick, then corrosion defense
    sticks it out a bit longer (but no longer than the weakest link in the
chain).

   Few ("never" say all) things evade corrosion.
   Stainless corrodes, even moly-alloy stainless corrodes.

   galvanized pipe:  not accepted in Mist Systems by FM
   for the very reason that one can not guarantee the plating has integrity
   across the entirety of a twenty-one foot stick.
   which begs the question, why are we specifying zinc plated pipe
   and not home-rule, old-school Sch 40 black-steel?


Scot Deal
Excelsior Fire Protection
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to