IDOD used to be UL listed and FM approved for use for 1¼" through 2" piping.  
Lat I heard, they were trying to get listing through 4".  However, I can't find 
it on FM Global's listing site.  Why is it not available in the US currently?  
I used it on a project 6 yrs ago with great success.

Ryan Hinson
Burns & McDonnell
Direct: 952-656-6003 Ext 3662

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Church
Sent: Tuesday, February 01, 2011 10:35 AM
To: [email protected]
Subject: RE: Butterfly vs. Gate valves: corrosion

Ironically, Allied had trade names of Armadillo and GatorShield at some point 
for piping products.

However, at this point IDOD pipe is not available in the USA; they are working 
on getting making it available here, date not set.

We'd used it- and as anyone who has seen it- it is a completely different 
product than conventional hot-dipped galvy.
In a class by itself and we look forward to its return.

glc


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Tuesday, February 01, 2011 10:48 AM
To: [email protected]
Subject: Re: Butterfly vs. Gate valves: corrosion

Does it have alligators on it?


At 10:31 AM 2/1/2011, you wrote:
>There is Izod pipe. The manufacturing system, for lack of a better 
>description, kind of semi alloys the zinc with the steel in layers.
>
>On Tue, Feb 1, 2011 at 7:19 AM, Mark Sornsin <[email protected]> wrote:
> > Scott:
> >
> > I don't know if this was already addressed - but to your point
> about zinc coated pipe.  We specify it over schedule 40, at least in 
> dry-pipe systems, because it performs better than schedule 40.  Yes, 
> galvanized piping will corrode eventually; but not nearly as fast as 
> black pipe (in a dry system). But maybe as importantly, the level of 
> scale build-up will be considerably smaller. The more scale build-up, 
> the more opportunity for scale to dislodge during
> system activation and obstruct flowing sprinklers.   FM still 
> prefers galvanized steel to black on dry and preaction systems, though 
> they'll accept black steel when the system 'air' pressure is 
> maintained with an inert gas. THAT may be the ideal solution, if you 
> can get the owner to spend the money on an inert gas system.
> >
> > Mark A. Sornsin, PE| Fire Protection Engineer Ulteig Engineers, 
> > Inc.| Fargo, ND [email protected]
> >
> >
> > ------------------------------------------------------
> >  galvanized pipe:  not accepted in Mist Systems by FM
> >   for the very reason that one can not guarantee the plating has integrity
> >   across the entirety of a twenty-one foot stick.
> >   which begs the question, why are we specifying zinc plated pipe
> >   and not home-rule, old-school Sch 40 black-steel?
> >
> >
> > Scot Deal
> > Excelsior Fire Protection
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: 
> > [email protected]
> >
> > To Unsubscribe, send an email 
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
>--
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis 
>Bacon, essayist, philosopher, and statesman (1561-1626) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to