Telecom is low voltage and although many architects refer to these compartments 
as "Electrical Rooms", I don't believe it's the intent of the code to require 
the same restrictions and observation of dedicated space as in rooms containing 
switch gear, high voltage, etc.
 
 

________________________________

From: [email protected] on behalf of Brad Casterline
Sent: Sun 1/30/2011 8:13 AM
To: [email protected]
Subject: RE: Electrical Rooms-Dedicated Equipment Space,Sprinklers and IBC 
Exemptions



Ron, I'll defer too, but the way I read it, it is even for telephone
switchboard type panels!


-----Original Message-----
From: Ron Greenman [mailto:[email protected]]
Sent: Sunday, January 30, 2011 10:07 AM
To: [email protected]
Subject: Re: Electrical Rooms-Dedicated Equipment Space,Sprinklers and IBC
Exemptions

Brad,

I'll defer to John if he calls me on this, but I don't think those
little electrical closets with a single lighting/general purpose
sub-panel, a mop sink, and the custodian's collection of porn really
count at all, and certainly not for sprinklers.

On Sun, Jan 30, 2011 at 8:01 AM, Brad Casterline
<[email protected]> wrote:
> It always does help, John, thanks, far more than 'stay out of the air
> space'...). I wanted to add for Brian's sake of the original post- it
> sounded like he had the many small electrical closets in mind- I offset
> around them and stub in a sidewall on my way by. I consider them OHI, and
so
> I can use standard response, intermediate temp. For the big elect. rooms,
> (and elevator equipment) I go in once and never come out :)
>
> -----Original Message-----
> From: John Drucker [mailto:[email protected]]
> Sent: Sunday, January 30, 2011 6:37 AM
> To: [email protected]
> Subject: FW: Electrical Rooms-Dedicated Equipment Space,Sprinklers and IBC
> Exemptions
>
> Members,
>
> Sprinkler piping is permitted in and through electrical rooms with two
> provisions, first the piping cannot be located in the dedicated electrical
> space, and second watersheds or other protective devices must be provided
> for electrical equipment below when piping is located above the dedicated
> electrical space.
>
> The National Electrical Code (NEC) does not prohibit the installation of
> fire sprinklers in electrical rooms, the 2006 and 2009 Editions of the IBC
> reinforce the sprinkler requirements;
>
> 903.3.1.1.1 Exempt locations. "Automatic sprinklers shall not be required
in
> the following rooms or areas where such rooms or areas are protected with
an
> approved automatic fire detection system in accordance with Section 907.2
> that will respond to visible or invisible particles of combustion.
> SPRINKLERS SHALL NOT BE OMITTED FROM ANY ROOM MERELY BECAUSE IT is damp,
of
> fire-resistance-rated construction OR CONTAINS ELECTRICAL EQUIPMENT."
>
> However the 2006 and 2009 IBC provides the following sprinkler exemption
for
> separated and detected GENERATOR AND TRANSFORMER rooms;
>
> 903.3.1.1. - 3. "GENERATOR AND TRANSFORMER ROOMS separated from the
> remainder of the building by walls and floor/ceiling or roof/ceiling
> assemblies having a fire-resistance rating of NOT LESS THAN 2 HOURS."
>
> Keep in mind where this exemption is utilized a fire alarm system pursuant
> to 907.2 utilizing smoke detectors located in the generator and or
> transformer room(s) must be installed which means the space must be
suitable
> for smoke detectors in accordance with the products listing and NFPA-72.
>
> Hope this helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
>
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and
approvals
> from Authority(s) Having Jurisdiction.
>
> -----Original Message-----
> Sent: Saturday, January 29, 2011 7:55 PM
> Subject: RE: Electrical Rooms
>
> 2008 NFPA-70 (NEC) 110.26(F)
>
> (F) Dedicated Equipment Space. All switchboards, panelboards, distribution
> boards, and motor control centers shall be located in dedicated spaces and
> protected from damage.
>
> (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through
> (F)(1)(d).
>
> (a) Dedicated Electrical Space. The space equal to the width and depth of
> the equipment and extending from the floor to a height of 1.8 m (6 ft)
above
> the equipment or to the structural ceiling, whichever is lower, shall be
> dedicated to the electrical installation. No piping, ducts, leak
protection
> apparatus, or other equipment foreign to the electrical installation shall
> be located in this zone.
>
> Exception: Suspended ceilings with removable panels shall be permitted
> within the 1.8-m (6-ft) zone.
>
> (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by
> 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided
> PROTECTION IS INSTALLED to
> avoid damage to the electrical equipment from condensation, LEAKS, OR
BREAKS
> IN SUCH FOREIGN SYSTEMS.
>
> (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the
> dedicated space where the piping complies with this section.
>
> (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does
> not add strength to the building structure shall not be considered a
> structural ceiling.
>
>
> In other words the dedicated equipment space is a three dimensional
> exclusion zone above and around switchboards, panelboards, distribution
> boards, and motor control centers which is reserved for electrical wiring
> only. The space begins at the floor, the width and depth of the equipment
> and to a height of 6ft above the equipment or to the STRUCTURAL ceiling
> whichever is LOWER. So keep out unless you're the electrician.
>
> Take heed of (C), the operative term is PROTECTION not PIPING. So you can
> spray water in the dedicated space, just don't run the pipe in there.
>
> Hope this helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
>
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and
approvals
> from Authority(s) Having Jurisdiction.
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to