Ron,

Didn't mean for it to come across that way, just trying to help out

John

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Ron Greenman
Sent: Sunday, January 30, 2011 1:08 PM
To: [email protected]
Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and IBC
Exemptions

I stand corrected. Although I haven't spent enough time with this to
know how corrected I've been but there's enough easily assimilable to
know I've been at least somewhat corrected. Thank you once again.

On Sun, Jan 30, 2011 at 9:49 AM, John Drucker <[email protected]>
wrote:
> Fear not for the answer you seek is found in the code
> ...............Emphasis in CAPS
>
> 2008 NFPA-70 (NEC)
>
> 110.26(F) Dedicated Equipment Space.
> "All SWITCHBOARDS, PANELBOARDS, DISTRIBUTION BOARDS, AND MOTOR CONTROL
> CENTERS shall be located in dedicated spaces and protected from damage."
>
> Article 100 Definitions
>
> Motor Control Center. An assembly of one or more enclosed sections having
a
> common power bus and PRINCIPALLY CONTAINING MOTOR CONTROL UNITS.
>
> Panelboard. A single panel or group of panel units designed for assembly
in
> the form of a single panel, including buses and automatic overcurrent
> devices, and equipped with or without switches FOR THE CONTROL OF LIGHT,
> HEAT, OR POWER CIRCUITS; designed to be placed in a cabinet or cutout box
> placed in or against a wall, partition, or other support, and ACCESSIBLE
> ONLY FROM THE FRONT.
>
> Switchboard. A large single panel, frame, or assembly of panels on which
are
> mounted on the face, back, or both, SWITCHES, OVERCURRENT AND OTHER
> PROTECTIVE DEVICES, BUSES, and usually instruments. Switchboards are
> GENERALLY ACCESSIBLE FROM THE REAR AS WELL as from the front and are not
> intended to be installed in cabinets.
>
> No definition for Distribution Boards......let's see if another article
> provides the answer..........
>
> 408.1 Scope. “This article covers the following: (1) All switchboards,
> panelboards, and DISTRIBUTION BOARDS INSTALLED FOR THE CONTROL OF LIGHT
AND
> POWER CIRCUITS.”
>
> 90.3 Code Arrangement. “This Code is divided into the introduction and
nine
> chapters, as shown in Figure 90.3. CHAPTERS 1, 2, 3, AND 4 APPLY
GENERALLY.”
>
> And last but not least, an online resource with descriptions, photos, etc
of
> panelboards, distribution boards from NEMA
>
> http://www.nema.org/prod/be/lvde/panelboard/enclose-pd/
>
> Hope this helps,
>
> John Drucker, CET
> Fire Protection Subcode Official
> Fire/Building/Electrical Inspector
> Fire Marshals Office
> Borough of Red Bank, NJ
>
> Not the official position of any agency, association, committee or
> otherwise.  Obtain required applications, permits, inspections and
approvals
> from Authority(s) Having Jurisdiction.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron
Greenman
> Sent: Sunday, January 30, 2011 11:07 AM
> To: [email protected]
> Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and
IBC
> Exemptions
>
> Brad,
>
> I'll defer to John if he calls me on this, but I don't think those
> little electrical closets with a single lighting/general purpose
> sub-panel, a mop sink, and the custodian's collection of porn really
> count at all, and certainly not for sprinklers.
>
> On Sun, Jan 30, 2011 at 8:01 AM, Brad Casterline
> <[email protected]> wrote:
>> It always does help, John, thanks, far more than 'stay out of the air
>> space'...). I wanted to add for Brian's sake of the original post- it
>> sounded like he had the many small electrical closets in mind- I offset
>> around them and stub in a sidewall on my way by. I consider them OHI, and
> so
>> I can use standard response, intermediate temp. For the big elect. rooms,
>> (and elevator equipment) I go in once and never come out :)
>>
>> -----Original Message-----
>> From: John Drucker [mailto:[email protected]]
>> Sent: Sunday, January 30, 2011 6:37 AM
>> To: [email protected]
>> Subject: FW: Electrical Rooms-Dedicated Equipment Space,Sprinklers and
IBC
>> Exemptions
>>
>> Members,
>>
>> Sprinkler piping is permitted in and through electrical rooms with two
>> provisions, first the piping cannot be located in the dedicated
electrical
>> space, and second watersheds or other protective devices must be provided
>> for electrical equipment below when piping is located above the dedicated
>> electrical space.
>>
>> The National Electrical Code (NEC) does not prohibit the installation of
>> fire sprinklers in electrical rooms, the 2006 and 2009 Editions of the
IBC
>> reinforce the sprinkler requirements;
>>
>> 903.3.1.1.1 Exempt locations. "Automatic sprinklers shall not be required
> in
>> the following rooms or areas where such rooms or areas are protected with
> an
>> approved automatic fire detection system in accordance with Section 907.2
>> that will respond to visible or invisible particles of combustion.
>> SPRINKLERS SHALL NOT BE OMITTED FROM ANY ROOM MERELY BECAUSE IT is damp,
> of
>> fire-resistance-rated construction OR CONTAINS ELECTRICAL EQUIPMENT."
>>
>> However the 2006 and 2009 IBC provides the following sprinkler exemption
> for
>> separated and detected GENERATOR AND TRANSFORMER rooms;
>>
>> 903.3.1.1. - 3. "GENERATOR AND TRANSFORMER ROOMS separated from the
>> remainder of the building by walls and floor/ceiling or roof/ceiling
>> assemblies having a fire-resistance rating of NOT LESS THAN 2 HOURS."
>>
>> Keep in mind where this exemption is utilized a fire alarm system
pursuant
>> to 907.2 utilizing smoke detectors located in the generator and or
>> transformer room(s) must be installed which means the space must be
> suitable
>> for smoke detectors in accordance with the products listing and NFPA-72.
>>
>> Hope this helps,
>>
>> John Drucker, CET
>> Fire Protection Subcode Official
>> Fire/Building/Electrical Inspector
>>
>> Not the official position of any agency, association, committee or
>> otherwise.  Obtain required applications, permits, inspections and
> approvals
>> from Authority(s) Having Jurisdiction.
>>
>> -----Original Message-----
>> Sent: Saturday, January 29, 2011 7:55 PM
>> Subject: RE: Electrical Rooms
>>
>> 2008 NFPA-70 (NEC) 110.26(F)
>>
>> (F) Dedicated Equipment Space. All switchboards, panelboards,
distribution
>> boards, and motor control centers shall be located in dedicated spaces
and
>> protected from damage.
>>
>> (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a)
through
>> (F)(1)(d).
>>
>> (a) Dedicated Electrical Space. The space equal to the width and depth of
>> the equipment and extending from the floor to a height of 1.8 m (6 ft)
> above
>> the equipment or to the structural ceiling, whichever is lower, shall be
>> dedicated to the electrical installation. No piping, ducts, leak
> protection
>> apparatus, or other equipment foreign to the electrical installation
shall
>> be located in this zone.
>>
>> Exception: Suspended ceilings with removable panels shall be permitted
>> within the 1.8-m (6-ft) zone.
>>
>> (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by
>> 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided
>> PROTECTION IS INSTALLED to
>> avoid damage to the electrical equipment from condensation, LEAKS, OR
> BREAKS
>> IN SUCH FOREIGN SYSTEMS.
>>
>> (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the
>> dedicated space where the piping complies with this section.
>>
>> (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that
does
>> not add strength to the building structure shall not be considered a
>> structural ceiling.
>>
>>
>> In other words the dedicated equipment space is a three dimensional
>> exclusion zone above and around switchboards, panelboards, distribution
>> boards, and motor control centers which is reserved for electrical wiring
>> only. The space begins at the floor, the width and depth of the equipment
>> and to a height of 6ft above the equipment or to the STRUCTURAL ceiling
>> whichever is LOWER. So keep out unless you're the electrician.
>>
>> Take heed of (C), the operative term is PROTECTION not PIPING. So you can
>> spray water in the dedicated space, just don't run the pipe in there.
>>
>> Hope this helps,
>>
>> John Drucker, CET
>> Fire Protection Subcode Official
>> Fire/Building/Electrical Inspector
>>
>> Not the official position of any agency, association, committee or
>> otherwise.  Obtain required applications, permits, inspections and
> approvals
>> from Authority(s) Having Jurisdiction.
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology
> Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
> They are happy men whose natures sort with their vocations. -Francis
> Bacon, essayist, philosopher, and statesman (1561-1626)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________