Tut, tut, Ron !

Boswell has two 'll's' !

(Dr Johnson wuld not mind  - his spelin wos atroshious)

Stewart (MA and MSc)


On 31 Jan 2011, at 00:28, Ron Greenman wrote:

> John, 
> 
> Not at all. I believe I asked for your further input regarding my comments. 
> To stand corrected is to admit learning in the face of preconceived notions. 
> The learning is good for us unwashed, the validation let's you know that your 
> efforts are appreciated, and the suggested lesson for the egotists is pretty 
> clear, though it may escape them due to their nature. If any apologies are 
> required it's from the developers of this form of communication wherein there 
> is no place for even inflection. Were that we were all Voltaire, Twain, or 
> Faulkner and there'd be no misunderstandings of this kind. But, alas, the art 
> of letter writing is long dead. Modern Boswels compiling the emails of even 
> famous scientists could easily title the work "The Collected Grocery Lists of 
> Dr. X." When it cost a man a week's pay to send a letter because it 
> absolutely, positively had to get there in a couple of months folks were a 
> little more erudite. I believe I'm near the last graduating class where 
> penmanship, spelling, punctuation, and an adherence to grammar were necessary 
> for the educated man. The term for an educated person used to be knowledge of 
> Arts, Letters and the Sciences. 
> 
> Ron Greenman 
> ...On the phone
> 
> On Jan 30, 2011, at 2:11 PM, "John Drucker" <[email protected]> wrote:
> 
>> Ron,
>> 
>> Didn't mean for it to come across that way, just trying to help out
>> 
>> John
>> 
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron Greenman
>> Sent: Sunday, January 30, 2011 1:08 PM
>> To: [email protected]
>> Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and IBC
>> Exemptions
>> 
>> I stand corrected. Although I haven't spent enough time with this to
>> know how corrected I've been but there's enough easily assimilable to
>> know I've been at least somewhat corrected. Thank you once again.
>> 
>> On Sun, Jan 30, 2011 at 9:49 AM, John Drucker <[email protected]>
>> wrote:
>>> Fear not for the answer you seek is found in the code
>>> ...............Emphasis in CAPS
>>> 
>>> 2008 NFPA-70 (NEC)
>>> 
>>> 110.26(F) Dedicated Equipment Space.
>>> "All SWITCHBOARDS, PANELBOARDS, DISTRIBUTION BOARDS, AND MOTOR CONTROL
>>> CENTERS shall be located in dedicated spaces and protected from damage."
>>> 
>>> Article 100 Definitions
>>> 
>>> Motor Control Center. An assembly of one or more enclosed sections having
>> a
>>> common power bus and PRINCIPALLY CONTAINING MOTOR CONTROL UNITS.
>>> 
>>> Panelboard. A single panel or group of panel units designed for assembly
>> in
>>> the form of a single panel, including buses and automatic overcurrent
>>> devices, and equipped with or without switches FOR THE CONTROL OF LIGHT,
>>> HEAT, OR POWER CIRCUITS; designed to be placed in a cabinet or cutout box
>>> placed in or against a wall, partition, or other support, and ACCESSIBLE
>>> ONLY FROM THE FRONT.
>>> 
>>> Switchboard. A large single panel, frame, or assembly of panels on which
>> are
>>> mounted on the face, back, or both, SWITCHES, OVERCURRENT AND OTHER
>>> PROTECTIVE DEVICES, BUSES, and usually instruments. Switchboards are
>>> GENERALLY ACCESSIBLE FROM THE REAR AS WELL as from the front and are not
>>> intended to be installed in cabinets.
>>> 
>>> No definition for Distribution Boards......let's see if another article
>>> provides the answer..........
>>> 
>>> 408.1 Scope. “This article covers the following: (1) All switchboards,
>>> panelboards, and DISTRIBUTION BOARDS INSTALLED FOR THE CONTROL OF LIGHT
>> AND
>>> POWER CIRCUITS.”
>>> 
>>> 90.3 Code Arrangement. “This Code is divided into the introduction and
>> nine
>>> chapters, as shown in Figure 90.3. CHAPTERS 1, 2, 3, AND 4 APPLY
>> GENERALLY.”
>>> 
>>> And last but not least, an online resource with descriptions, photos, etc
>> of
>>> panelboards, distribution boards from NEMA
>>> 
>>> http://www.nema.org/prod/be/lvde/panelboard/enclose-pd/
>>> 
>>> Hope this helps,
>>> 
>>> John Drucker, CET
>>> Fire Protection Subcode Official
>>> Fire/Building/Electrical Inspector
>>> Fire Marshals Office
>>> Borough of Red Bank, NJ
>>> 
>>> Not the official position of any agency, association, committee or
>>> otherwise.  Obtain required applications, permits, inspections and
>> approvals
>>> from Authority(s) Having Jurisdiction.
>>> 
>>> 
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Ron
>> Greenman
>>> Sent: Sunday, January 30, 2011 11:07 AM
>>> To: [email protected]
>>> Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and
>> IBC
>>> Exemptions
>>> 
>>> Brad,
>>> 
>>> I'll defer to John if he calls me on this, but I don't think those
>>> little electrical closets with a single lighting/general purpose
>>> sub-panel, a mop sink, and the custodian's collection of porn really
>>> count at all, and certainly not for sprinklers.
>>> 
>>> On Sun, Jan 30, 2011 at 8:01 AM, Brad Casterline
>>> <[email protected]> wrote:
>>>> It always does help, John, thanks, far more than 'stay out of the air
>>>> space'...). I wanted to add for Brian's sake of the original post- it
>>>> sounded like he had the many small electrical closets in mind- I offset
>>>> around them and stub in a sidewall on my way by. I consider them OHI, and
>>> so
>>>> I can use standard response, intermediate temp. For the big elect. rooms,
>>>> (and elevator equipment) I go in once and never come out :)
>>>> 
>>>> -----Original Message-----
>>>> From: John Drucker [mailto:[email protected]]
>>>> Sent: Sunday, January 30, 2011 6:37 AM
>>>> To: [email protected]
>>>> Subject: FW: Electrical Rooms-Dedicated Equipment Space,Sprinklers and
>> IBC
>>>> Exemptions
>>>> 
>>>> Members,
>>>> 
>>>> Sprinkler piping is permitted in and through electrical rooms with two
>>>> provisions, first the piping cannot be located in the dedicated
>> electrical
>>>> space, and second watersheds or other protective devices must be provided
>>>> for electrical equipment below when piping is located above the dedicated
>>>> electrical space.
>>>> 
>>>> The National Electrical Code (NEC) does not prohibit the installation of
>>>> fire sprinklers in electrical rooms, the 2006 and 2009 Editions of the
>> IBC
>>>> reinforce the sprinkler requirements;
>>>> 
>>>> 903.3.1.1.1 Exempt locations. "Automatic sprinklers shall not be required
>>> in
>>>> the following rooms or areas where such rooms or areas are protected with
>>> an
>>>> approved automatic fire detection system in accordance with Section 907.2
>>>> that will respond to visible or invisible particles of combustion.
>>>> SPRINKLERS SHALL NOT BE OMITTED FROM ANY ROOM MERELY BECAUSE IT is damp,
>>> of
>>>> fire-resistance-rated construction OR CONTAINS ELECTRICAL EQUIPMENT."
>>>> 
>>>> However the 2006 and 2009 IBC provides the following sprinkler exemption
>>> for
>>>> separated and detected GENERATOR AND TRANSFORMER rooms;
>>>> 
>>>> 903.3.1.1. - 3. "GENERATOR AND TRANSFORMER ROOMS separated from the
>>>> remainder of the building by walls and floor/ceiling or roof/ceiling
>>>> assemblies having a fire-resistance rating of NOT LESS THAN 2 HOURS."
>>>> 
>>>> Keep in mind where this exemption is utilized a fire alarm system
>> pursuant
>>>> to 907.2 utilizing smoke detectors located in the generator and or
>>>> transformer room(s) must be installed which means the space must be
>>> suitable
>>>> for smoke detectors in accordance with the products listing and NFPA-72.
>>>> 
>>>> Hope this helps,
>>>> 
>>>> John Drucker, CET
>>>> Fire Protection Subcode Official
>>>> Fire/Building/Electrical Inspector
>>>> 
>>>> Not the official position of any agency, association, committee or
>>>> otherwise.  Obtain required applications, permits, inspections and
>>> approvals
>>>> from Authority(s) Having Jurisdiction.
>>>> 
>>>> -----Original Message-----
>>>> Sent: Saturday, January 29, 2011 7:55 PM
>>>> Subject: RE: Electrical Rooms
>>>> 
>>>> 2008 NFPA-70 (NEC) 110.26(F)
>>>> 
>>>> (F) Dedicated Equipment Space. All switchboards, panelboards,
>> distribution
>>>> boards, and motor control centers shall be located in dedicated spaces
>> and
>>>> protected from damage.
>>>> 
>>>> (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a)
>> through
>>>> (F)(1)(d).
>>>> 
>>>> (a) Dedicated Electrical Space. The space equal to the width and depth of
>>>> the equipment and extending from the floor to a height of 1.8 m (6 ft)
>>> above
>>>> the equipment or to the structural ceiling, whichever is lower, shall be
>>>> dedicated to the electrical installation. No piping, ducts, leak
>>> protection
>>>> apparatus, or other equipment foreign to the electrical installation
>> shall
>>>> be located in this zone.
>>>> 
>>>> Exception: Suspended ceilings with removable panels shall be permitted
>>>> within the 1.8-m (6-ft) zone.
>>>> 
>>>> (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by
>>>> 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided
>>>> PROTECTION IS INSTALLED to
>>>> avoid damage to the electrical equipment from condensation, LEAKS, OR
>>> BREAKS
>>>> IN SUCH FOREIGN SYSTEMS.
>>>> 
>>>> (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the
>>>> dedicated space where the piping complies with this section.
>>>> 
>>>> (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that
>> does
>>>> not add strength to the building structure shall not be considered a
>>>> structural ceiling.
>>>> 
>>>> 
>>>> In other words the dedicated equipment space is a three dimensional
>>>> exclusion zone above and around switchboards, panelboards, distribution
>>>> boards, and motor control centers which is reserved for electrical wiring
>>>> only. The space begins at the floor, the width and depth of the equipment
>>>> and to a height of 6ft above the equipment or to the STRUCTURAL ceiling
>>>> whichever is LOWER. So keep out unless you're the electrician.
>>>> 
>>>> Take heed of (C), the operative term is PROTECTION not PIPING. So you can
>>>> spray water in the dedicated space, just don't run the pipe in there.
>>>> 
>>>> Hope this helps,
>>>> 
>>>> John Drucker, CET
>>>> Fire Protection Subcode Official
>>>> Fire/Building/Electrical Inspector
>>>> 
>>>> Not the official position of any agency, association, committee or
>>>> otherwise.  Obtain required applications, permits, inspections and
>>> approvals
>>>> from Authority(s) Having Jurisdiction.
>>>> 
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> For Technical Assistance, send an email to: [email protected]
>>>> 
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>> 
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>> 
>>>> For Technical Assistance, send an email to: [email protected]
>>>> 
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>> 
>>> 
>>> 
>>> 
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>> 
>>> [email protected]
>>> 
>>> http://www.bates.ctc.edu/fireprotection/
>>> 
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>> 
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>>> 
>>> They are happy men whose natures sort with their vocations. -Francis
>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> 
>>> For Technical Assistance, send an email to: [email protected]
>>> 
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>> 
>>> For Technical Assistance, send an email to: [email protected]
>>> 
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>> 
>> 
>> 
>> 
>> -- 
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering Technology
>> Bates Technical College
>> 1101 So. Yakima Ave.
>> Tacoma, WA 98405
>> 
>> [email protected]
>> 
>> http://www.bates.ctc.edu/fireprotection/
>> 
>> 253.680.7346
>> 253.576.9700 (cell)
>> 
>> Member:
>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>> 
>> They are happy men whose natures sort with their vocations. -Francis
>> Bacon, essayist, philosopher, and statesman (1561-1626)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> For Technical Assistance, send an email to: [email protected]
>> 
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> 
>> For Technical Assistance, send an email to: [email protected]
>> 
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to