Craig,
I agree with your statements below as they apply to your situation, and I guess 
you and I have different perspectives and interpretations because we have 
different jobs...you being a contractor and me being an AHJ.
The opinions that I provided were for only as they apply to my jurisdiction 
which does not include North or South Carolina.
rick

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 01, 2011 4:02 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

Unfortunately per the building codes there are occupancies where sprinklers are 
not required and 8.1.1 would not be applicable.  For example I have had office 
areas which were required to be sprinklered either by owner or underwriter 
request and to serve that area I had to pass through an unsprinklered F-2 
occupancy.  The F-2 didn't require sprinklers so I have no grounds to apply 
8.1.1.  I have sprinklered S-1 Storage rooms which were within S-2 areas with 
the proper physical separation.  Again Main running through non-sprinklered 
area to get to sprinklered area.

As far as pump house, if it's an electric pump, no sprinklers required, 
although fire separation required between pump room and adjacent occupancies if 
pump room within a building. Sprinklers required as specifically referenced 
only for diesel primarily due to the diesel fuel hazard located within the pump 
house.

I'm not going to even talk about plastic pipe in a warehouse.  

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matsuda, Richard
Sent: Tuesday, February 01, 2011 4:47 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

It's 8.1.1 in both the 2007 and 2010 editions.
Item (1) "Sprinklers shall be installed throughout the premises."

The handbook commentary explains that fire in unsprinklered areas could spread 
and grow into sprinklered areas. Partial protection is not recommended. If you 
intend to install the sprinkler riser and the feed main in an unsprinklered 
area, and run the piping into the adjoining sprinklered space, then fire in the 
unsprinklered space may compromise the main before the sprinklers have the 
chance to operate.

This is the same reasoning as requiring sprinklers in a detached fire pump 
house or not allow exposed plastic piping in warehouse occupancies. You must 
protect the piping and equipment in order that they will function during a fire 
condition. Maybe you can enclose the piping in a 2-hour chase or use some kind 
of fire-wrap to protect it...or even install sprinklers 10-ft O.C. along the 
length of the main to spot protect it...maybe.
This might be allowed with approval of the AHJ and all parties involved with 
the property.

rick matsuda
city of dallas

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of 
[email protected]
Sent: Tuesday, February 01, 2011 3:36 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

What edition?  2007, I'm not seeing anything related to the question.

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Matsuda, Richard
Sent: Tuesday, February 01, 2011 4:30 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

Try par. 8.1.1.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, February 01, 2011 3:24 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

Craig-
Right on, I knew that wasn't the section I was thinking of but was the
closest thing I could find. Are you aware of any code that prohibits running
sprinkler pipe through unprotected areas?

Brian Harris
FDFP Inc.
 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, February 01, 2011 4:09 PM
To: [email protected]
Subject: RE: Protection of Sprinkler Pipe

That section is for fire service mains that would be run aboveground, not
interior sprinkler piping.  Say a building was built on top of the
underground fire main and someone decided to just rise up and run it inside
the building and then back down and reconnect to the UG main instead of
going around the building and staying underground.  That's what that section
is dealing with.   

Craig L. Prahl, CET   
Fire Protection 
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Tuesday, February 01, 2011 4:02 PM
To: [email protected]
Subject: Protection of Sprinkler Pipe

I thought I read in NFPA that sprinkler piping cannot pass through areas of
a building that did not have sprinkler protection, the closest thing I could
find was 8.16.4.3. Maybe I'm thinking of plastic pipe? Any ideas?

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to