Craig, I agree with your statements below as they apply to your situation, and I guess you and I have different perspectives and interpretations because we have different jobs...you being a contractor and me being an AHJ. The opinions that I provided were for only as they apply to my jurisdiction which does not include North or South Carolina. rick
-----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, February 01, 2011 4:02 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe Unfortunately per the building codes there are occupancies where sprinklers are not required and 8.1.1 would not be applicable. For example I have had office areas which were required to be sprinklered either by owner or underwriter request and to serve that area I had to pass through an unsprinklered F-2 occupancy. The F-2 didn't require sprinklers so I have no grounds to apply 8.1.1. I have sprinklered S-1 Storage rooms which were within S-2 areas with the proper physical separation. Again Main running through non-sprinklered area to get to sprinklered area. As far as pump house, if it's an electric pump, no sprinklers required, although fire separation required between pump room and adjacent occupancies if pump room within a building. Sprinklers required as specifically referenced only for diesel primarily due to the diesel fuel hazard located within the pump house. I'm not going to even talk about plastic pipe in a warehouse. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matsuda, Richard Sent: Tuesday, February 01, 2011 4:47 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe It's 8.1.1 in both the 2007 and 2010 editions. Item (1) "Sprinklers shall be installed throughout the premises." The handbook commentary explains that fire in unsprinklered areas could spread and grow into sprinklered areas. Partial protection is not recommended. If you intend to install the sprinkler riser and the feed main in an unsprinklered area, and run the piping into the adjoining sprinklered space, then fire in the unsprinklered space may compromise the main before the sprinklers have the chance to operate. This is the same reasoning as requiring sprinklers in a detached fire pump house or not allow exposed plastic piping in warehouse occupancies. You must protect the piping and equipment in order that they will function during a fire condition. Maybe you can enclose the piping in a 2-hour chase or use some kind of fire-wrap to protect it...or even install sprinklers 10-ft O.C. along the length of the main to spot protect it...maybe. This might be allowed with approval of the AHJ and all parties involved with the property. rick matsuda city of dallas -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, February 01, 2011 3:36 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe What edition? 2007, I'm not seeing anything related to the question. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Matsuda, Richard Sent: Tuesday, February 01, 2011 4:30 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe Try par. 8.1.1. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, February 01, 2011 3:24 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe Craig- Right on, I knew that wasn't the section I was thinking of but was the closest thing I could find. Are you aware of any code that prohibits running sprinkler pipe through unprotected areas? Brian Harris FDFP Inc. -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of [email protected] Sent: Tuesday, February 01, 2011 4:09 PM To: [email protected] Subject: RE: Protection of Sprinkler Pipe That section is for fire service mains that would be run aboveground, not interior sprinkler piping. Say a building was built on top of the underground fire main and someone decided to just rise up and run it inside the building and then back down and reconnect to the UG main instead of going around the building and staying underground. That's what that section is dealing with. Craig L. Prahl, CET Fire Protection CH2MHILL Lockwood Greene 1500 International Drive Spartanburg, SC 29304-0491 Direct - 864.599.4102 Fax - 864.599.8439 CH2MHILL Extension 74102 [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Brian Harris Sent: Tuesday, February 01, 2011 4:02 PM To: [email protected] Subject: Protection of Sprinkler Pipe I thought I read in NFPA that sprinkler piping cannot pass through areas of a building that did not have sprinkler protection, the closest thing I could find was 8.16.4.3. Maybe I'm thinking of plastic pipe? Any ideas? Brian Harris First Defense Fire Protection 11957 Ramah Church Road Huntersville, NC 28078 Phone: 704.948.3506 Fax: 704.948.3507 Nicet # 128476 ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770) http://www.pctools.com/ ======= ======= Email scanned by PC Tools - No viruses or spyware found. (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16770) http://www.pctools.com/ ======= _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)