13 8.6.5.2.1.5 is is for obstructions less than or equal to18" below
the deflector (see 13 8.6.5.2.1.1) and refers to pattern development.
8.6.5.1.2 option 2 is a subsection of 8.6.5.1 and refers to the hazard
being shielded from from water reaching it. 13 8.6.5.2.1.5 is about
developing the umbrella and where it will go and what might block it
while 8.6.5.1.2 option 2 is about a horizontal obstruction that
creates a water shadow on the floor.

On Wed, Feb 9, 2011 at 9:49 AM, Smith, Steven D. (CSFD)
<[email protected]> wrote:
> For a coworker...
>
>
>
> Subject: 2010 NFPA 13 8.6.5.2.1.5
>
>
>
> Can anyone shed some light on this section?  It seems to contradict
> section 8.6.5.1.2 option 2.
>
>
>
> Does the size of the obstruction not matter?
>
>
>
> I have a convention center with 55-inch diameter lights that are 2-feet
> deep.  The sprinkler contactor is using the referenced section to avoid
> dropping a head inside the light to cover below it (as it is built, we
> can pipe though the fixture and use a concealed head).
>
>
>
> Any thoughts?
>
>
>
> Doreen E. Withee
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to