Actually, it was quarter center point of light; had to miss the bulb thingy and 
all.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, February 09, 2011 2:18 PM
To: [email protected]
Subject: RE: FW: 2010 NFPA 13 8.6.5.2.1.5

You mean you've never designed a system to center of light?


At 04:04 PM 2/9/2011, you wrote:
>Now, now George, this is a serious discussion-:)
>
>BK
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of George 
>Church
>Sent: Wednesday, February 09, 2011 1:15 PM
>To: [email protected]
>Subject: RE: FW: 2010 NFPA 13 8.6.5.2.1.5
>
>Maybe this could set a precedent for a UL Listed heat baffle for 
>sprinklers too far down from the roof deck?
>Test with and without the bulb.
>
>George Church
>Rowe Sprinkler Systems, Inc.
>PO Box 407, Middleburg, PA 17842
>877-324-ROWE       570-837-6335 fax
>[email protected]
>
>
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Thom
>Sent: Wednesday, February 09, 2011 2:39 PM
>To: [email protected]
>Subject: RE: FW: 2010 NFPA 13 8.6.5.2.1.5
>
>The first question I would ask, before I even thought about installing 
>ANY kind of sprinkler head inside of a U/L listed light fixture is what 
>happens to that u/l listing?
>My next thought is --- Well I won't say nuts but really you can't mean 
>that you want someone to drill a listed light fixture to install a 
>sprinkler head inside of its lamp shade or shell??? Really????
>
>I could see having 4 equally spaced sprinkler heads located around the 
>fixture, but inside??? Really???
>
>Obviously there must be more to this than just that, there always is. 
>Like height of sprinkler pipe to the light fixture? Height of fixture 
>above floor? Sprinkler density? SSP or SSU or EC sprinklers?? Distance 
>from roof to Light? Distance from roof to Sprinklers? Type of 
>construction? Concrete, steel, beam open joist, twin tee?????
>
>It just seems that D. Withee may not be using as much common sense as 
>she is known for. There has to be a better way. One last question? Is 
>this coming up at plan review? Or final?? If you missed it at plan 
>review when the options were less impactful of everyone, you need to 
>exercise your authority carefully, and it should be tempered with how 
>to make this as painless for everyone, since you missed it in plan 
>review.
>
>Just one former contractors point of view.
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Ron 
>Greenman
>Sent: Wednesday, February 09, 2011 12:06 PM
>To: [email protected]
>Subject: Re: FW: 2010 NFPA 13 8.6.5.2.1.5
>
>13 8.6.5.2.1.5 is is for obstructions less than or equal to18" below 
>the deflector (see 13 8.6.5.2.1.1) and refers to pattern development.
>8.6.5.1.2 option 2 is a subsection of 8.6.5.1 and refers to the hazard 
>being shielded from from water reaching it. 13 8.6.5.2.1.5 is about 
>developing the umbrella and where it will go and what might block it 
>while 8.6.5.1.2 option 2 is about a horizontal obstruction that creates 
>a water shadow on the floor.
>
>On Wed, Feb 9, 2011 at 9:49 AM, Smith, Steven D. (CSFD) 
><[email protected]> wrote:
> > For a coworker...
> >
> >
> >
> > Subject: 2010 NFPA 13 8.6.5.2.1.5
> >
> >
> >
> > Can anyone shed some light on this section?  It seems to contradict 
> > section 8.6.5.1.2 option 2.
> >
> >
> >
> > Does the size of the obstruction not matter?
> >
> >
> >
> > I have a convention center with 55-inch diameter lights that are 
> > 2-feet deep.  The sprinkler contactor is using the referenced 
> > section to avoid dropping a head inside the light to cover below it 
> > (as it is built, we can pipe though the fixture and use a concealed head).
> >
> >
> >
> > Any thoughts?
> >
> >
> >
> > Doreen E. Withee
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: 
> > [email protected]
> >
> > To Unsubscribe, send an email
> > to:[email protected]
> > (Put the word unsubscribe in the subject field)
> >
>
>
>
>--
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis 
>Bacon, essayist, philosopher, and statesman (1561-1626) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to