Is the FDC connected to pump suction?
If its not, and the pump is producing 150 PSI discharge, and the FD hits the 
FDC with 150 (connected to the discharge side of the fire pump), then you have 
150 PSI, not 300, going to the system.

You can graph the combination of dissimilar supplies by graphing both and 
adding the flows at same pressures.

Safe to assume the large Fed entity has an FPE as EOR? Cause the FDC isn't 
exactly an "automatic" water supply, so the ice is thin, even if its up by the 
FroBros.

George Church
Rowe Sprinkler Systems, Inc.
PO Box 407, Middleburg, PA 17842
877-324-ROWE       570-837-6335 fax
[email protected]



-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Greg McGahan
Sent: Monday, March 07, 2011 12:29 PM
To: [email protected]
Subject: Manual vs Auto SP

What do you do with an existing SP system that far exceed the pressure 
requirement when performing calcs...nearly 200 psi over the curve due to the 
fact that you are flowing 1,250 gpm through 4" pipe.

The owner wants to classify the system as MANUAL and utilize a FD to feed the 
system but  leave the fire pump connected. The system still does not work when 
using only the FDC feeding the system due to the fact that the FD only plans to 
utilize 2 each 2-1/2" hose to connect to the FDC.

The owner - a large Federal Entity - wants to make this a HYBRID system 
utilizing the Fire Pump and the FDC combined. I can't find a correct way to do 
this...thoughts?

Greg

--
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to