Thanks Cecil and Pete- I have wondered about this, and if I had bet, I would
have lost- It seemed like unprotected floor space, but with heads across the
top, it is not unprotected, it just takes a while for the water to get
there.

-----Original Message-----
From: Sprinkler Academy - C Bilbo [mailto:[email protected]] 
Sent: Friday, March 11, 2011 11:30 AM
To: FORUM
Subject: RE: Sprinkler under first accessible landing


Posting this for my good friend from Florida.
 

Cecil Bilbo 
Academy of Fire Sprinkler Technology
Parkland College
 
 
From: Pete Schwab
Subject: RE: Sprinkler under first accessible landing
 
See recent action taken at the ROP meeting in Savannah
2013 NFPA 13 ROP
Proposal 13-247 (Log #329)
Accept
Add Section 8.15.3.2.3.1 Sprinklers shall be permitted to be omitted from
beneath landings or stairways where the space under the stairs is blocked
off so that storage cannot occur.
Substantiation - The concept of eliminating the sprinkler at the bottom of
the stairs has always been implied by NFPA 13, but the statement needs to be
made more explicit for most AHJ's. Where the egress path is the only
available space in the stairwell, sprinklers should not be necessary.



 
> Subject: RE: Sprinkler under first accessible landing
> Date: Fri, 11 Mar 2011 07:51:12 -0500
> From: [email protected]
> To: [email protected]
> 
> Cory, the 13 handbook explains it a little better, saying it is because
> storage can be put under the lowest landing and thus the requirement for
> a sprinkler at top as well as under the lowest landing, exhibit 8.29 of
> the handbook shows where the head is required.
> 
> Richard Carr, SET
> Design Manager
> Associated Sprinkler Co., LLC
> 336.373.3901 ext 217
> [email protected]
> 
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Dewayne
> Martinez
> Sent: Friday, March 11, 2011 7:41 AM
> To: [email protected]
> Subject: RE: Sprinkler under first accessible landing
> 
> Cory,
> When I hear "first accessible landing" I picture the landing directly
> above the lowest exit door way. I do not think it has anything to do
> with a access panel. I put the sprinklers in the ceiling at the top of
> the shaft and under the first accessible landing. 
> 
> Dewayne Martinez
> Design Build Fire Protection
> New Berlin, WI
> 
> 
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Cory
> Power
> Sent: Friday, March 11, 2011 6:19 AM
> To: [email protected]
> Subject: Sprinkler under first accessible landing
> 
> I have an an engineer asking to provide a sprinkler under the first
> landing of a non-combustible stairwell. The spec for the job states that
> "Sprinkler shall be installed at top of shaft. Space below first landing
> is considered concealed, non-accessible, non-combustible, and hence does
> not require sprinkler protection."
> 
> he engineer who is reviewing my plans sent me an email stating the
> following:
> 
> *8.15.3.2 Noncombustible Construction.*
> 
> *8.15.3.2.1 *In noncombustible stair shafts having noncombustible stairs
> with noncombustible or limited-combustible finishes, sprinklers shall be
> installed at the top of the shaft and under the first
> accessible*landing*above the bottom of the shaft.
> 
> We always took this to mean the sprinklers are required under the first
> landing? And by accessible we took this to mean access could be provided
> by a access panel.."
> 
> Is this the way I should be interpreting the code? Do I still have to
> sprinkler under the landing and make sure there's an access hatch? or
> should I be able to omit it like the spec indicates?
> 
> I have been following this forum for a while now. This is the first
> question I have posted.
> 
> 
> - Cory
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email
> to:[email protected]
> (Put the word unsubscribe in the subject field)
> 
> 
> This email and any attached files are confidential and intended solely for
the intended recipient(s). If you are not the named recipient you should not
read, distribute, copy or alter this email. Any views or opinions expressed
in this email are those of the author and do not represent those of the
company. Warning: Although precautions have been taken to make sure no
viruses are present in this email, the company cannot accept responsibility
for any loss or damage that arise from the use of this email or attachments.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> 
> For Technical Assistance, send an email to: [email protected]
> 
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
                                          
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to