But Kevin gets graded as incompetent for misspelling incompetent
(incopitent) (and I almost incompetently misspelled the way he misspelled 
incompetent). :0)

On Fri, Mar 11, 2011 at 7:59 AM,  <[email protected]> wrote:
> We don't bash anyone PE or non-PE who has interest in this forum for 
> the sake of learning.  It's those who think they know it all and have 
> no desire to learn or listen that we like to barbeque.  ;)
>
> Active participation that has educational value is always welcome and 
> encouraged.
>
> Stuff showing how dumb or arrogant some people are also provides 
> entertainment value which we need now and then as well.
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Law, 
> Kevin W
> Sent: Friday, March 11, 2011 10:55 AM
> To: [email protected]
> Subject: RE: Sprinkler under first accessible landing
>
> Be gentle, now.........I appreciate that you said only "no gold star" instead 
> of going off on a rant about incopitent engineers.  Some of us do try to 
> learn and willing to listen to reason........
>
>
> Kevin Law, PE
> Sr. Fire Protection Engineer
> HVAC/Fire Protection, M&PE
> Bechtel National - WTP Project
> Ph.   509-371-3280
> Cell   509-531-5715
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of 
> [email protected]
> Sent: Friday, March 11, 2011 5:39 AM
> To: [email protected]
> Subject: RE: Sprinkler under first accessible landing
>
> Under the lowest landing due to the possibility of that space being used for 
> storage.  If the space is totally enclosed then there is no access for 
> storage and no head is required if the stair is non-combustible.  The spec is 
> correct.  <sigh> The Engineer has taken some license on his quote of the 13 
> section.  The word "accessible" is not in the script.  So no gold star for 
> him.
>
>
> NFPA 13, 2007 - 8.15.3.2.1 "In noncombustible stair shafts having 
> noncombustible stairs with noncombustible or limited combustible finishes, 
> sprinklers shall be installed at the top of the shaft and under the first 
> landing above the bottom of the shaft."
>
> Craig L. Prahl, CET
> Fire Protection
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> CH2MHILL Extension  74102
> [email protected]
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Cory 
> Power
> Sent: Friday, March 11, 2011 7:19 AM
> To: [email protected]
> Subject: Sprinkler under first accessible landing
>
> I have an an engineer asking to provide a sprinkler under the first 
> landing of a non-combustible stairwell. The spec for the job states 
> that "Sprinkler shall be installed at top of shaft. Space below first 
> landing is considered concealed, non-accessible, non-combustible, and 
> hence does not require sprinkler protection."
>
> he engineer who is reviewing my plans sent me an email stating the
> following:
>
> *8.15.3.2 Noncombustible Construction.*
>
> *8.15.3.2.1 *In noncombustible stair shafts having noncombustible 
> stairs with noncombustible or limited-combustible finishes, sprinklers 
> shall be installed at the top of the shaft and under the first 
> accessible*landing*above the bottom of the shaft.
>
> We always took this to mean the sprinklers are required under the 
> first landing? And by accessible we took this to mean access could be 
> provided by a access panel.."
>
> Is this the way I should be interpreting the code? Do I still have to 
> sprinkler under the landing and make sure there's an access hatch? or 
> should I be able to omit it like the spec indicates?
>
> I have been following this forum for a while now. This is the first 
> question I have posted.
>
>
> - Cory
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626) 
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to