With this little pipe velocity is the problem. I'm using the bigger
holes to require less pressure at the end head and so slow the water
down that's passing through the narrow pipe. Given the restriction of
the pipe and the constant calculated demand of 0.15/X (900 or 1500)
this may do nothing but my in head estimator isn't well calibrated
either.

On Mon, Apr 4, 2011 at 10:09 AM, Morey, Mike <[email protected]> wrote:
> K8 heads could actually penalize his design in the OH-I area couldn't they?  
> 7 psi minimum end head dictates 14ish GPM out of a k5.6, even at 130 sq ft 
> going to a K8 head would actually cause him to discharge more GPM than the 
> density requires (at least using my not particularly well calibrated internal 
> calculator), and GPM as we know is what creates friction loss.  In the LH 
> area if he spaced the heads out near the limits a K8 will save him some 
> pressure, but given his water supply that doesn't look to be his biggest 
> concern.  The big question is how long the 1 1/4" run is in my mind, if it's 
> short enough you can jump up at the connection, if it isn't then you don't 
> have a lot of options unless maybe you can squeeze out some area reductions 
> (QR/Ceiling height reductions if they haven't been considered) with careful 
> code reading and head selection.
>
> Mike Morey, SET
> Sprinkler Designer
> BMW Constructors, Inc.
> O: 317.651.0596 | C: 317.439.2695
> www.bmwc.com 
> <https://owa.bmwc.com/exchweb/bin/redir.asp?URL=http://www.bmwc.com>
>
>
> ________________________________
>
> From: [email protected] on behalf of Ron Greenman
> Sent: Mon 4/4/2011 12:49 PM
> To: [email protected]
> Subject: Re: Design solution needed
>
>
>
> What K heads are you using. Bigger holes help more than bigger pipes
> in good pressure/bad water situations. If you're using K5.6 see the
> huge gain K8.0 will give you. And your moister recent post asked most
> of the questions I asked just as that left and yours arrived.
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to