where are you getting the idea that you can divide the kitchen into
two 400 sf compartments and legitimately call it light hazard? Pipe
type and hose demand is allowed to use LH (though for hose demand, the
rooms can not be adjacent so that nixes reducing it).
Roland
On Apr 4, 2011, at 10:40 AM, Joel Chaim wrote:
I'm thinking of offering them to divide the kitchen area into 2
compartments
less than 400 sq ft. this way we can utilize the same hazard as the
dining
area my question can we lower the density to .10 as well because
NFPA states
that regardless if utilize the hose demand or not you still need to
calc.
1500 sq ft. even the room is less.