What Ron said but realize these are only listed for 165 PSI, not 175, plus
they have a 10 PSI differential.  Don't forget the relief downstream.
TD


Depending on the applicable edition of NFPA 14 you may have to use two PRV's
in series with bypass instead of just one but is still okay to do. You need
to check NFPA 14, I believe it changed to require two PVC's in series in
2007. If you're on 2004 only one valve is required.


Ron Fletcher
Aero Automatic
Phoenix, AZ

 