What Ron said but realize these are only listed for 165 PSI, not 175, plus they have a 10 PSI differential. Don't forget the relief downstream. TD
Depending on the applicable edition of NFPA 14 you may have to use two PRV's in series with bypass instead of just one but is still okay to do. You need to check NFPA 14, I believe it changed to require two PVC's in series in 2007. If you're on 2004 only one valve is required. Ron Fletcher Aero Automatic Phoenix, AZ _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)