Should add that depending on the downstream flows, you may well have
FOUR PRV's in two series pairs.   Any time you use a pressure control or
reducing valve, it is imperative to verify both the maximum and MINIMUM
flow rates that the device is rated for.   Downstream of a pump serving
a combined standpipe system, you may have a maximum flow rate of
750-1000 GPM for the standpipe system and we're brain-trained to go
right to the 6" appliances.   But if it's also serving a sprinkler
system, a 6" valve requires at least a 100gpm flow to be properly set
and to function normally.   In those cases, you need to manifold a pair
of smaller valves that will function down to the flow rate of a single
sprinkler.

My opinion only - read the book on your own,

SML




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Tom
Duross
Sent: Friday, May 06, 2011 5:18 AM
To: [email protected]
Subject: RE: Pressure reducing valves in pump discharge

What Ron said but realize these are only listed for 165 PSI, not 175,
plus
they have a 10 PSI differential.  Don't forget the relief downstream.
TD


Depending on the applicable edition of NFPA 14 you may have to use two
PRV's
in series with bypass instead of just one but is still okay to do. You
need
to check NFPA 14, I believe it changed to require two PVC's in series in
2007. If you're on 2004 only one valve is required.


Ron Fletcher
Aero Automatic
Phoenix, AZ

 



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)