I just ran into a similar situation.

If you use a pressure reducing valve (after the pump control valve) it must 
have it's own control valve and a means of testing the pressure reducing valve 
at sprinkler flow.

 Jimmy Waite, CET
 Design Engineer                                                                
           
 [email protected]
 mobile: 919.622.7030 


   3609 Bastion Lane  |  Raleigh, NC  27604  |  : 919.212.2356  |  : 
919.212.2357  |  www.piedmontfire.com


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Friday, May 06, 2011 7:18 AM
To: [email protected]; [email protected]
Subject: RE: Pressure reducing valves in pump discharge

Thank you, that makes sense. 

Bobby Gillett
Sr. Project Manager
Key Fire Protection, Inc.
(731) 424-0130 office  (731) 424-9285 fax 
(731) 267-4853 cell
[email protected]
 
 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Travis Mack,
SET
Sent: Thursday, May 05, 2011 3:51 PM
To: [email protected]
Subject: Re: Pressure reducing valves in pump discharge

If I recall correctly, you can't have the PRedV before the pump 
discharge valve as NFPA 20 does not allow PRedV's.  However, NFPA 13 
does, so by placing it after the pump discharge shut off valve, you are 
now in NFPA 13 territory and not NFPA 20 territory.

A.4.7.7.2 It is not the intent of this subsection to restrict the use
of pressure reducing valves downstream of the discharge isolation
valve for the purpose of meeting the requirements of 4.7.7.

4.7.7.1 The net pump shutoff (churn) pressure plus the maximum
static suction pressure, adjusted for elevation, shall not exceed
the pressure for which the system components are rated.
4.7.7.2* Pressure relief valves and pressure regulating devices
in the fire pump installation shall not be used as a means to
meet the requirements of 4.7.7.1.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to