Where does the 12" restriction come from?

At 02:47 PM 6/24/2011, you wrote:
>If you go with 2 grates to permit air flow, the temperature in the channel
>should be closer to the room side of the insulation than that on the other
>side of the insulation. I would be concerned if there were no grates. Make
>sure you don't use plastic piping, as otherwise there will be an additional
>restriction of having a head within 12 inches of the grates.
>
>Tony 
>
>-----Original Message-----
>From: [email protected]
>[mailto:[email protected]] On Behalf Of Todd Williams
>Sent: June 24, 2011 8:15 AM
>To: [email protected]
>Subject: Channel in roof joists
>
>Sorry, forgot title
>
>At 10:09 AM 6/24/2011, you wrote:
>>I am working on a small mixed-use building with commercial space on the 
>>first floor and an apartment with loft above. Part of the apartment has 
>>a cathedral ceiling, which needs to have sprinklers on the slope. No 
>>other options. The roof is framed with 2x10s and they plan to use a 
>>spray in foam insulation the entire depth of the joists. My thought was 
>>if they took one joist bay and only put 5" of insulation and create a 
>>space to run the pipe. Would that be sufficient to prevent pipe from 
>>freezing? I also thought about putting a small grate at the bottom and 
>>top of the channel to allow heat to flow into the space. Has anyone 
>>done anything like that before? Thoughts on weather it would work? Not 
>>a lot of options and I don't want to go with an antifreeze system
>>
>>Todd G. Williams, PE
>>Fire Protection Design/Consulting
>>Stonington, CT
>>860.535.2080
>>www.fpdc.com
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email 
>>to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
>Todd G. Williams, PE
>Fire Protection Design/Consulting
>Stonington, CT
>860.535.2080
>www.fpdc.com
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to