NFPA13, 2010 edition
11.1.6 Hose Allowance.
11.1.6.1 An allowance for inside and outside hose shall not be
required where tanks supply sprinklers only.

Jarron J. Gass - J. & J. Fire Protection Co., Inc.
101 Powell Rd., Butler, PA 16002, 
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, June 29, 2011 3:15 PM
To: [email protected]
Subject: Re: Hose Stream

Perhaps those in the fire service could answer this better, but I'll give my
thought. My take is that our designs are to provide sprinkler protection
plus one or two hose streams to a fire prior to the fire department
augmenting the water supply (except for systems with pumps that equal or
exceed the pumps in their trucks)  If that is the case, the hose stream
calculation needs to be included. If the pump is large, the hose streams
would be needed as part of the overall fire protection plan. So yes, you
have to include them. 


At 02:53 PM 6/29/2011, you wrote:
>Back to an old question but a little different. Tank with sufficient 
>capacity to supply duration for both a yard hydrant and the sprinkler 
>system. Pump sufficient to supply required psi to the sprinks and meet 
>the AHJ's requirement at the hydrant. Question: When calculating the 
>sprinks do I need to add the 250 gpm hose allowance on that demand 
>curve? This seems to be a 'safety cushion" for a water supply 
>controlled by an outside party such as a municipality. This is not the 
>case here wherein the quantity of water and delivery pressures are 
>completely controlled: a closed versus open system if you will.
>
>--
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis 
>Bacon, essayist, philosopher, and statesman (1561-1626) 
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to