Lets start over again since I think the birds have already grabbed the bread crumbs.

You have a supply tank for both sprinklers and hydrants. After the pump, the hydrant and sprinkler paths diverge. Do you need to add the hose demand to the sprinkler calc - right? What difference would this be from a street main supplying both? The two tank comparison is the same as two separate municipal supplies feeding each. I must be missing something since I see no potential confusion so take another stab at 'splainin'.

Roland


On Jun 29, 2011, at 12:59 PM, Ron Greenman wrote:

Right and that is accounted for. I can flow both hydrant and sprinks
simultaneously for the total duration of each. I may or may not need a
pumper at the hydrant. This is actually more of a pressure question and is just theoretical. If the hose stream portion of the sprinkler demand crosses the the supply curve from the pump so I don't have the required flow at with the hose stream but there is more on-site water than I need to flow both (and that is not subject to demand fluctuations from other users) I can adjust my pump curve. The question though is why should I need to add that demand on the sprinkler calc where the supply to the sprinks and the supply to the hydrant diverge? This is akin to doing a rack calc and an overhead calc and then adding an arbitrary extra amount of gpm at the common point of divergence from the main after you've balanced the two. There's no problem to overcome since in the actual case the hose demand can be added without causing the problem but it did bring up the question of why does it need inclusion in the first place under these conditions. The obvious parent answer is because I (the code) say. All the exceptions are for process water and when there are only sprinklers on the tank. If I had a small elevated tank for the sprinks only and another for the hydrant only I wouldn't have to include hose stream but when I combine the both in the same tank I do.
Doesn't make sense to me.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to