Have you considered an automatic fire door?

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
130 w 9th Ave.
North Kansas City, MO 64116

*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Wednesday, August 03, 2011 2:28 PM
To: [email protected]
Subject: RE: Unprotected Opening

I know they now have specific sprinklers listed for glazing protection. But
if you look at the test reports that came out when the tests were done
initially, they used standard quick response sprinklers. The flows were also
higher than that for the listed heads. 

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: August 3, 2011 12:01 PM
To: [email protected]
Subject: RE: Unprotected Opening

Glazing protection for two hour ratings is only achieved by the use of a
specific listed sprinkler.  That sprinkler has very specific installation
requirements and again TWO HOURS.  We have a Three hour wall here.

If you try to apply the criteria for exposure protection out of 13, what
K-factor at what pressure provides protection equivalent to a 3-hour
separation?

Craig L. Prahl, CET   
Fire Protection
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Wednesday, August 03, 2011 12:47 PM
To: [email protected]
Subject: RE: Unprotected Opening

It looks to me they want a deluge water curtain for the opening. I would use
the guidelines for glazing protection, keeping in mind it is generally for
two hour rating, whereas you may need for three hours. The problem I see is
if one side is already sprinklered, you might have to add the new deluge
water curtain to the design area of the existing ceiling system adjacent to
the opening. That might be tough depending on your safety factors.

Tony 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: August 3, 2011 10:01 AM
To: [email protected]
Subject: Re: Unprotected Opening

This recommendation came from somewhere (ie insurance company). Find the
source and start asking there. 


At 11:39 AM 8/3/2011, you wrote:
>We have an industrial project with a 3hr firewall separating two areas. 
>On one side of the fire wall has no protection at the roof per its 
>industrial rating and on the other side is a paint area protected as EH 
>GroupII (.40/2500). The 3hr firewall has an opening (40'-0wX20'-0h) 
>where product passes through from one side to the other. We are being 
>asked to put sprinklers on the non protected side of the opening 
>supplied by a deluge system. Apparently I am overlooking the 
>requirements (spacing, density, etc.); where would I find these 
>requirements or would I simply use the requirements of the protected side -
.40/2500 spaced at max 12'-0?
>
> 
>
>Thank you,
>
> 
>
>Bobby Gillett
>
>Sr. Project Manager
>
>Key Fire Protection, Inc.
>
>(731) 424-0130 office  (731) 424-9285 fax
>
>(731) 267-4853 cell
>
> <mailto:[email protected]>
>[email protected]
>
> 
>
> 
>
> 
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to