There is no requirement to check pitch in NFPA-25. It is assumed that system was properly installed. I would suggest if you feel there has been building settlement or some other reason you feel there may be a problem it makes sense to check but this would be outside scope of 25 inspection and should be qualified as such.
Top Myers Myers Risk Services PO Box 741 Kimberton, PA 19442 O - 484-924-8155 C - 610-952-0965 [email protected] Providing Solutions For Your Risk Management Needs -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of David de Vries Sent: Wednesday, August 24, 2011 6:01 PM To: AFSA SprinklerForum Subject: Dry Pipe System Pitch Inspection Somewhere I remember seeing a requirement that the pitch of dry pipe systems must be periodically checked, like at a 5 year or 10 year interval. When I went looking for it in 25, I could not find it. Did I imagine this, or is it actually out there somewhere? Thanks. Dave David A. de Vries, P.E., CSP Firetech Engineering Incorporated -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachments/20110824/0aaaaf20/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum