There is no requirement to check pitch in NFPA-25. It is assumed that system 
was properly installed.  I would suggest if you feel there has been building 
settlement or some other reason you feel there may be a problem it makes sense 
to check but this would be outside scope of 25 inspection and should be 
qualified as such. 

Top Myers
Myers Risk Services
PO Box 741
Kimberton, PA 19442
O - 484-924-8155  C - 610-952-0965
[email protected]

Providing Solutions For Your Risk Management  Needs


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of David de Vries
Sent: Wednesday, August 24, 2011 6:01 PM
To: AFSA SprinklerForum
Subject: Dry Pipe System Pitch Inspection

Somewhere I remember seeing a requirement that the pitch of dry pipe systems 
must be periodically checked, like at a 5 year or 10 year interval.  When I 
went looking for it in 25, I could not find it.  Did I imagine this, or is it 
actually out there somewhere?
 
Thanks.

Dave 

David A. de Vries, P.E., CSP 
Firetech Engineering Incorporated 