I mean to say that if you peruse the manufacturer's data sheets for products like CPVC and PEX they require it in very clear language. I believe that the press-type fittings do as well. Not in every case - Jamie alluded to the fitting chart in NFPA 13 for example.
Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bob Sent: Friday, September 23, 2011 11:45 AM To: [email protected] Subject: RE: "flow through tee's and Hydraulic calculations" I either misunderstand what is being said here, or my ignorance is about to show through, but I have never heard anyone say that "you absolutely have to include" a flow through tee in calculations regardless of type. 13 22.4.4.7(5) seems clear to me that you don't include this fitting regardless of schedule. Am I missing something? Thanks, Bob Knight, CET III 208-318-3057 www.firebyknight.com -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Steve Leyton Sent: Friday, September 23, 2011 12:13 PM To: [email protected] Subject: RE: "flow through tee's and Hydraulic calculations" Manufacturer's data sheets give the values and instruct on use - see BlazeMaster design guide, for ex. Yes, you absolutely have to include ... Steve Leyton -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Seidl Jamie D. Sent: Friday, September 23, 2011 10:11 AM To: [email protected] Subject: "flow through tee's and Hydraulic calcultions" Hello forumites, I'd like to pole the forum and see what the consensus is on accounting for flow through tee's or "tee on the run" when calculating a system. NFPA states that they do not need to be included when using the schedule 40 fitting table. But when using manufactures' fitting equivalents, do you include them? -------------- next part -------------- An HTML attachment was scrubbed... URL: <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attach ments/20110923/dfa2b426/attachment.html> _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum